D

demkap

hi there,

would appreciate advise please...
im carrying out a condition report on a church and have found a number of interesting issues. i found quite a few DBs with asbestos in the fuse carriers... would you give this a C2 code even though they aren't being disturbed?

also found a 40amp breaker with a 6mm and a 2.5mm cable going into it.. what code would you advise for this?

also a ring circuit with a 3rd cable going into the 32amp breaker... i was thinking a C2?

emergency lights dont come on under fault conditions?

no rcd protection throughout but not likely to have equipment plugged in outside C3?

metal conduit being used as a CPC but i seem to be getting good continuity readings?

single socket having a ZS of 8ohms!? why would this be the case aswell... bad earth?

much appreciated

dem
 
Every coded observation you list should reference a regulation in BS7671.


  • Asbestos in equipment ..... is this under the scope and remit of an EICR ?

  • 2.5mm cable protected by 40A OCPD ...... what is the connected load ? Could it comply if the regulations for omission for overload and fault protection were taken into account ?
  • emg lighting ....... As point 1, is this within the remit of your report ?
  • I would agree with C3 for no additional protection in this case.
  • What's non compliant or dangerous about a metal conduit as a CPC ?
  • Obviously further investigation needed.
 
Every coded observation you list should reference a regulation in BS7671.


  • Asbestos in equipment ..... is this under the scope and remit of an EICR ? i do believe it is up to the duty holder, the person ordering the work to get this sorted. would it be worth noting down maybe as further investigation on the report?

  • 2.5mm cable protected by 40A OCPD ...... what is the connected load ? Could it comply if the regulations for omission for overload and fault protection were taken into account ? its supplying a DB board which has over 6 circuits on it...



  • emg lighting ....... As point 1, is this within the remit of your report ? youre right but worth a mention?
  • I would agree with C3 for no additional protection in this case.
  • What's non compliant or dangerous about a metal conduit as a CPC ? nothing just obviously you need to have good continuity readings? i was told that any socket outlets that are using the conduit as the cpc would still need to have earthing( cables) as protection?
  • Obviously further investigation needed.

so the circuit with 3 cables in it would not comply either and be a C2 code or FI?
 

Reply to Eicr codes help in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
True. Although I'd hazard a guess that things like woodworm treatment are probably chemically quite similar? Don't know.
Replies
13
Views
1K
  • Question
If they got a shock then something cannot have been isolated.
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top