demkap

hi there,

would appreciate advise please...
im carrying out a condition report on a church and have found a number of interesting issues. i found quite a few DBs with asbestos in the fuse carriers... would you give this a C2 code even though they aren't being disturbed?

also found a 40amp breaker with a 6mm and a 2.5mm cable going into it.. what code would you advise for this?

also a ring circuit with a 3rd cable going into the 32amp breaker... i was thinking a C2?

emergency lights dont come on under fault conditions?

no rcd protection throughout but not likely to have equipment plugged in outside C3?

metal conduit being used as a CPC but i seem to be getting good continuity readings?

single socket having a ZS of 8ohms!? why would this be the case aswell... bad earth?

much appreciated

dem
 
OP, please don't take this the wrong way, but should you really be doing Periodic Inspections?
Some of your queries are very simple - for example, possibly giving a Code to a conduit'ed accessory - really?
You should know all of the answers to your queries if you had the relevant experience, please, learn a bit more before you offer to do any more, as it is, you are coming across as very inexperienced, and it woudlnt look good if a Client started querying your assumptions.
 
But on the other hand there's no harm in seeking a little reassurance and guidance from fellow electricians, none of us know it all ! [With possibly one or two exceptions on here :innocent:]

Thank you Dave :clap:
 

Reply to Eicr codes help in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
True. Although I'd hazard a guess that things like woodworm treatment are probably chemically quite similar? Don't know.
Replies
13
Views
1K
  • Question
If they got a shock then something cannot have been isolated.
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top