D
demkap
hi there,
would appreciate advise please...
im carrying out a condition report on a church and have found a number of interesting issues. i found quite a few DBs with asbestos in the fuse carriers... would you give this a C2 code even though they aren't being disturbed?
also found a 40amp breaker with a 6mm and a 2.5mm cable going into it.. what code would you advise for this?
also a ring circuit with a 3rd cable going into the 32amp breaker... i was thinking a C2?
emergency lights dont come on under fault conditions?
no rcd protection throughout but not likely to have equipment plugged in outside C3?
metal conduit being used as a CPC but i seem to be getting good continuity readings?
single socket having a ZS of 8ohms!? why would this be the case aswell... bad earth?
much appreciated
dem