I know but in #2 you say you weren't sure if you would Code it when it is a non-compliant means of installation.
Last edited:
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss EICR Codes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Correct.I know but in #2 you say you wouldn't Code it when it is a non-compliant means of installation.
I would disagree, how safe or unsafe something is isn't contingent on whether is was compliant or not previously, but wholly on does it or does it not present a danger.I agree the new Coding system is poor the old Catergories were better. Having said that the cable is not installed in compliance with BS7671 and comparing it with old conductor colours and all insulated consumer units isn't relevant, that is a case of a previous compliance no longer satisfying current requirements. This cable installation has never been compliant, the fact it has rcd protection is irrelevant.
No one is upset here just pointing the OP in the right direction.Yes, and I would note the observation, but for me I would be unlikely to code it, if you would wish to then fine, no issue with that.
Dot see why you are getting upset.
Opinions vary.
Non compliance does not mandate a code, the risk/danger level does.
But anyone is free to code as they see fit, under the existing system, there is no standard (unlike mots and so on) hence why eicrs are so varied in quality.
Is there any evidence that this cable is NOT in a duct?
To establish if it is in a duct or deep enough to be unlikely to damaged by a garden fork maybe it should be an FI (Further Investigation)!Yes, the fact that I can see it disappearing into the ground with no sign of a duct, even after digging out a small amount of ground around it!!
If it was in a duct, it would have to be ducted all the way up to the surface, therefore no further investigation necessary.To establish if it is in a duct or deep enough to be unlikely to damaged by a garden fork maybe it should be an FI (Further Investigation)!
Agree.If it was in a duct, it would have to be ducted all the way up to the surface, therefore no further investigation necessary.
I wouldn't either, I would definitely go C2.Now that we have that subject well and truly covered, what about a TT installation with Ze of 1000ohms, tested in the middle of summer. Rod and connection etc looking in good condition.
Theoretically a 30ma RCD still disconnects, but I’m not sure I’d be happy with no code.
Not a problem I ever expect to come across round here though. It’s usually pretty easy to get well under 50ohms with even one rod. Usually more like 10-20ohms.
Reply to EICR Codes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net