My comments in red:

So just had a quick look. I've not really studied the codes but I'll give it a go with my limited knowledge.

First things I notice,

* Too much copper showing on the tails into RCD. C3- what is the issue here with all covers on?

* Too much copper on neutrals in neutral bar. C3 - what is the issue here with all covers on?

* Links between main isolator and RCD too small. C3 - would it matter what size they are? Also assuming they are too small what would be the danger?

* Exposed busbar. C2 - what is the issue here with all covers on?

* Tails wired into RCD and not main switch. C2 - Agree - good spot.

Can't work out if that 1.5mm2 on that 16A is showing signs of overload or it's a shadow? The breaker is too large for 1.5mm2.

Not really sure how to word it but the 2 neutral bars are not going to be acting as a split board of they are both linked together. Is that correct?

Also if that board is not isolated somewhere else it's actually still live (even though it appears to be isolated with the main switch) obviously due to the switched tails.
 
My comments in red:

Sorry for delay.

My answers.

* Possible short circuit.

* Possible short circuit.

* Csa would be based on the installation main cut out fuse. Similar to how you'd size tails. Too small and the conductors would be subject to overload.

* possible short circuit. The real danger would be if there was a missing Blanc or the cover was off for testing etc.
 
A small amount of exposed copper on the neutral conductors, is not really a problem when you consider the neutral bar is it’self exposed.
True, but this is the prime example of where it could be done better..... The time taken to do it neatly is minuscule and it shows that you take pride in the quality of your work.
 
True, but this is the prime example of where it could be done better..... The time taken to do it neatly is minuscule and it shows that you take pride in the quality of your work.
Yes, I don’t like exposed copper, even though I know it doesn’t make any odds.
Then again, I always tighten up any unused screws on the busbars, just in case they work loose and fall into an MCB.
 
My comments in red:
@gazdkw82 really think about why your coding them could it be that it could just be a comment on the EICR with no coding would suffice?
If you can back up your codings with Regs and feel it necessary to code then go for it. A handy tip when coding an EICR is to look at the inspection schedule on the IET model form the list is by no means exhaustive but it can give you a step to a hint for some of the more common situations you may come across.
 
Yes, I don’t like exposed copper, even though I know it doesn’t make any odds.
Then again, I always tighten up any unused screws on the busbars, just in case they work loose and fall into an MCB.
You need a winner badge for that alone. Last week I went to a property where A.N. Other “electrician” had plied their wares. Customer was complaining of a fishy smell coming from the CU nothing was tight looks like everything was terminated with fingertips not even the screws of occupied terminals were tight nevermind the unused ones. :eek: Anyway long story short the Main nuetral was arcing and Crispy as it wasn’t ever tight the sheathing and insulation had almost completely melted off inside the CU unfortunately though I ain’t got pics as I’d dropped my phone in a bloody puddle the day before:(
 
[ElectriciansForums.net] EICR Coding challenge for trainees.


1. Potential live accessible parts (assuming CU is live!). Depending upon location C1 or C2. Looks high to ceiling (don't know ceiling height) but probably a C2. C1 if low and easier access.

2. Lack of labelling either a C3 or just a comment (I normally use the phrase 'bag o rubbish' in the comments section :) ). I see circuits not labelled, no RCD label, no next inspection date label etc etc so I'd probably C3 it.

3. Mixed manufacturers parts. Can't work out the name on the RCD. (per IET and BEAMA guidelines) I'd C3 it. Apart from laziness/couldn't give a rubbish I dont know why the contractor didn't fit a Crabtree part?=
 

Reply to EICR Coding challenge for trainees. in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
340
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
877
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top