My comments in red:
So just had a quick look. I've not really studied the codes but I'll give it a go with my limited knowledge.
First things I notice,
* Too much copper showing on the tails into RCD. C3- what is the issue here with all covers on?
* Too much copper on neutrals in neutral bar. C3 - what is the issue here with all covers on?
* Links between main isolator and RCD too small. C3 - would it matter what size they are? Also assuming they are too small what would be the danger?
* Exposed busbar. C2 - what is the issue here with all covers on?
* Tails wired into RCD and not main switch. C2 - Agree - good spot.
Can't work out if that 1.5mm2 on that 16A is showing signs of overload or it's a shadow? The breaker is too large for 1.5mm2.
Not really sure how to word it but the 2 neutral bars are not going to be acting as a split board of they are both linked together. Is that correct?
Also if that board is not isolated somewhere else it's actually still live (even though it appears to be isolated with the main switch) obviously due to the switched tails.