r2 on a RFC, not continuous, but every socket has an earth & acceptable Zs. Code 2 or 3 (r1 & rn are fine)?:dunce2:
 
What does 543.2.9 say in its entirety. Word for word. I'm away from home and don't have my bgb?

Here you go
[ElectriciansForums.net] EICR coding disagreement....
 
So it only needs fixing if it's an easy job?

Yeeeehaaaaaa
i didn't mean easy. customer could refuse a quote or refuse carpets /flooring being lifted/damaged.
 
All, thanks for the views. The problem is not at a socket, these were all checked. The adiabatic equation indicates a cpc of 2mm with a pfc of 1.14kA:thinking:

This mid floor rental flat is fully floored in continuous laminate and the costs to lift and relay would be horrendous (never mind the cost/time to find the fault). Board has no spare ways, but I'm thinking 2, 20 amp radials may be the only way to go.The l/lord is not being difficult and I'm just trying to ensure a safe installation without costs being exhorbitant.
 
All, thanks for the views. The problem is not at a socket, these were all checked. The adiabatic equation indicates a cpc of 2mm with a pfc of 1.14kA:thinking:

This mid floor rental flat is fully floored in continuous laminate and the costs to lift and relay would be horrendous (never mind the cost/time to find the fault). Board has no spare ways, but I'm thinking 2, 20 amp radials may be the only way to go.The l/lord is not being difficult and I'm just trying to ensure a safe installation without costs being exhorbitant.

Assuming its T&E then it's a C2

As long as you can seperate the ring in the right place then that will work. Unless the fault is at a joint where a spur has been joined in as you will loose the spur when you disconnect that bit of cable.
 
Have you tried doing a Zs at all the sockets to see if there is a "jump" in the readings?

That's a good point M. Interestingly, there was very little variation in the values. It's quite a compact flat, not a large floor area.

Dave, there was already a spur with the cpc going nowhere - socket now disconnected, but it does suggest an under floor jb.
 
Even if the adiabatic equation showed compliance I would still be c3 with a further investigation required. We are supposed to ensure the install is safe for continued use ans conforms to at least bs7671....You don't just "loose" 1 conductor and do an equation and suddenly the disappearing conductor becomes of no consequence lol. It would bother me even more if it is wired in T+E then I would be even more concerned.
 
Even if the adiabatic equation showed compliance I would still be c3 with a further investigation required. We are supposed to ensure the install is safe for continued use ans conforms to at least bs7671....You don't just "loose" 1 conductor and do an equation and suddenly the disappearing conductor becomes of no consequence lol. It would bother me even more if it is wired in T+E then I would be even more concerned.

You've missed the point!

If the adiabatic shows that it does not comply as a cpc then it is a C2 as it is potentially dangerous.
If it shows that it does comply then it is not potentially dangerous but only non compliant with the regs so is a C3.

Why would you be more concerned if it's T&E ? A broken cpc is a broken cpc whatever the cable is made of
 
You've missed the point!

If the adiabatic shows that it does not comply as a cpc then it is a C2 as it is potentially dangerous.
If it shows that it does comply then it is not potentially dangerous but only non compliant with the regs so is a C3.

Why would you be more concerned if it's T&E ? A broken cpc is a broken cpc whatever the cable is made of
Well it would suggest that the fabric of the cable is broken somewhere and if it is not at an accessible point you would have to wonder how/why you have lost 1 core out of 3....I suppose a good IR test result could put your mind at rest.....don't mind me im sure I have some sort of OCD lol, sometimes it's helpful and sometimes its just a nuisance.
 
Well it would suggest that the fabric of the cable is broken somewhere and if it is not at an accessible point you would have to wonder how/why you have lost 1 core out of 3....I suppose a good IR test result could put your mind at rest.....don't mind me im sure I have some sort of OCD lol, sometimes it's helpful and sometimes its just a nuisance.

I would be far more concerned with SWA or MICC as it would logically be significant damage to loose the connection wheras with T&E it would far more likely be a single connection broken.
 

Reply to EICR coding disagreement.... in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

It’s difficult to advise on an electrical issue when some isn’t very conversant with electrical terminology.
Replies
14
Views
1K
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top