C3... improvement recommended. i'd be inclined to fix it if it could be done economically and without pulling up floors etc.
Reg 543.2.9 says that with the exception of metal enclosures or coverings used as a cpc the cpc must be run as a ring with both ends connected to the earthing terminal at the circuits origin
i didn't mean easy. customer could refuse a quote or refuse carpets /flooring being lifted/damaged.So it only needs fixing if it's an easy job?
Yeeeehaaaaaa
All, thanks for the views. The problem is not at a socket, these were all checked. The adiabatic equation indicates a cpc of 2mm with a pfc of 1.14kA:thinking:
This mid floor rental flat is fully floored in continuous laminate and the costs to lift and relay would be horrendous (never mind the cost/time to find the fault). Board has no spare ways, but I'm thinking 2, 20 amp radials may be the only way to go.The l/lord is not being difficult and I'm just trying to ensure a safe installation without costs being exhorbitant.
Have you tried doing a Zs at all the sockets to see if there is a "jump" in the readings?
Even if the adiabatic equation showed compliance I would still be c3 with a further investigation required. We are supposed to ensure the install is safe for continued use ans conforms to at least bs7671....You don't just "loose" 1 conductor and do an equation and suddenly the disappearing conductor becomes of no consequence lol. It would bother me even more if it is wired in T+E then I would be even more concerned.
Well it would suggest that the fabric of the cable is broken somewhere and if it is not at an accessible point you would have to wonder how/why you have lost 1 core out of 3....I suppose a good IR test result could put your mind at rest.....don't mind me im sure I have some sort of OCD lol, sometimes it's helpful and sometimes its just a nuisance.You've missed the point!
If the adiabatic shows that it does not comply as a cpc then it is a C2 as it is potentially dangerous.
If it shows that it does comply then it is not potentially dangerous but only non compliant with the regs so is a C3.
Why would you be more concerned if it's T&E ? A broken cpc is a broken cpc whatever the cable is made of
Well it would suggest that the fabric of the cable is broken somewhere and if it is not at an accessible point you would have to wonder how/why you have lost 1 core out of 3....I suppose a good IR test result could put your mind at rest.....don't mind me im sure I have some sort of OCD lol, sometimes it's helpful and sometimes its just a nuisance.
That would be in Chapter 54.Why a C3? We run ring final circuits in steel conduit and use that as a single earth.
Where is the reg that says r2 must be a ring?
That would be in Chapter 54.
Regulation 543.2.9.