Hello, I'm new to this forum. I'm not quite sure about RCD protection for a domestic dwellings - No RCD protection on circuits where cables are not buried to 50mm - I'm of the opinion its a code 3 however some colleagues are saying its a code 2 ( I cant find clarification on this ) - Any ideas? I don't want to over egg a report but at the same time want to be sure I'm giving the right advise
 
Regs are not retrospective so can only be a 3
Whilst I would consider this particular issue to be a C3, it certainly isn't the case that something which was compliant at the time of installation cannot be given a more severe observation than that where it clearly poses a danger. (My favourite example being fused neutrals.)
 
C3 unless passing through or supplying special locations, sockets with potential for outdoor use etc.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
rugeley
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Connect Midlands Ltd

Thread Information

Title
EICR coding domestic
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
5
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
STUARTSPARKY,
Last reply from
STUARTSPARKY,
Replies
5
Views
1,767

Advert

TrueNAS JBOD Storage Server

Back
Top