I assume you meant hob?

Rating plate states 5.7KW

5700/230 = 24.78A

even working at a more realistic:

5700/240 = 23.75A

As I suspected you haven't calculated the load correctly, you should be taking the first 10A of FLC plus 30% of the remainder.

Which gives the load as 14.1A rather than your 23.8A which makes it a small overload as per the regulation posted above, the 23.8A is not a small overload as it is nearly a 100% overload.
Now you just have to decide whether that is a sustained small overload or a short duration small overload.
If it is sustained I would say it is potentially dangerous.
If it is short duration then no problem.

Are you sure you should be carrying out EICRs if you don't know how to apply basic diversity calculations?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
West Yorkshire

Thread Information

Title
EICR Coding for hob wiring
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
27

Advert

Thread statistics

Created
ray-bentos,
Last reply from
Knobhead,
Replies
27
Views
5,506

Advert

TrueNAS JBOD Storage Server

Back
Top