I assume you meant hob?
Rating plate states 5.7KW
5700/230 = 24.78A
even working at a more realistic:
5700/240 = 23.75A
As I suspected you haven't calculated the load correctly, you should be taking the first 10A of FLC plus 30% of the remainder.
Which gives the load as 14.1A rather than your 23.8A which makes it a small overload as per the regulation posted above, the 23.8A is not a small overload as it is nearly a 100% overload.
Now you just have to decide whether that is a sustained small overload or a short duration small overload.
If it is sustained I would say it is potentially dangerous.
If it is short duration then no problem.
Are you sure you should be carrying out EICRs if you don't know how to apply basic diversity calculations?
West Yorkshire
EICR Coding for hob wiring
ray-bentos,
Knobhead,