I need a hand to confirm what coding goes with what please on this house
I have been asked to inspect a house by an agent and this is the situation:
- TN-S Earthing (0.4 ohms) No code.
- No CPC in lighting circuit with Class 1 fittings C2
- No Bonding to Gas or Water C2
- No Sleaving on any CPCs C3
- All CPCs twisted together and put into 1 conductor on MET (in CU) C3
- Main Earth has been extended using a 6mm black (neutral) cable C3
- 10 Sockets on a 20A Radial (2.5 T&E) No code
- CU inaccessible under Stairs Define inaccessible.....
- RCD as main switch (only 5 circuits) Whilst it maybe a pain under fault conditions, cant really assign a code to IMO.
- Trunking Missing exposing unsupported Cables Definne unsupported
- Extractor Fan in bathroom controlled by the shower circuit (no shower) on 6mm T&E 32A MCB More info needed
- No labels on CU apart from an old damaged RCD label (this circuit or part of it is protected by an RCD) C3
- Half a socket in the kitchen does not work (245v LE, 110v LN, 110v NE) Neutral issue, C2.
Rewire was done about 1 year ago in old (Red & Black) cables, not notified, no certificate - landlord said the electrician and gas fitter walked off site due to payment problems (not a clue)
Boiler is less than 1 year old - never been serviced or when it was installed
I know a few of these are not a cause for concern but they are there to draw the picture
Thanks for your help
Rewire was done about 1 year ago in old (Red & Black) cables, not notified, no certificate.
buy guidance note 3...don't be so lazy
nick...this is nowt uncommon fella...CUs ,service heads n gas in thick places......had old BS3036s under sinks in the corner of the cupboard a few times......CUs where they`v been `boxed in` to (make em look neater?)...except you cant get the front of......it just goes on and on....if in doubt..just blame a kitchen fitter...its always their fault..lol...In regards to inaccessible CU the gap under the stairs is only 2 foot high and you have to be on your bell to get to the CU, the head and meter is under there as well as the gas mains and meter.
completely stupid place to put the utility supplies if you ask me!