Interesting job doing a massive eicr on a factory
On a lot of the socket circuits the sockets are wired in singles in metallic trunking with the trunking being used as one of the cpc's it appears.

So two things are the trunking is also being used as cpc for lighting and some other circuits

And the drops from trunking to sockets are in plastic conduit with only one cpc in

Ideas on coding the above, can you use trunking to provide earthing for more than one circuit?

Also have quite a few boards and switchfuses fed direct from main switch incoming side i.e twinned with the incoming feed on another board coding ideas ?
 
OK, difficult, but off the top of my head I would test earth continuity and resistance from each socket back to MET or distribution panel, and if it is within limits It passes. If there is a variation in readings, time to start checking connections, best way is probably to flag it up as potentially dangerous and recommend running a cpc in the trunking.
 
Resistance is very low on every circuit major parallel earth paths maybe.
Zs all within as well.
Im more wondering about the 1 cpc on ring when socket circuit drops from trunking to socket outlets?
 
Hi SES,

"Im more wondering about the 1 cpc on ring when socket circuit drops from trunking to socket outlets?"

I am having a bit of a senior moment with the above statement, can you explain a bit more? How old is the install, and what are the general ambient conditions like. If it is clean dry and warm, it is unlikely to give problems, but persistent ambient moisture plays hell with trunking and vertical conduit drops.
 
I don't think it would be wise to run a separate trunking for each circuit lol "can you use trunking to provide earthing for more than one circuit?"
 
Haha yes amazing constructive answer, what i mean is can the trunking be allowed to provide the cpc for every circuit run within it
 
Sockets are a ring main 2x line 2x neutral and 2x cpc however the cpc is trunking as one leg and single as the other leg.
Now all the sockets are taken from the metal trunking in plastic conduit so at each socket outlet the is only one cpc not two as no path through the plastic conduit
 
I was asking if it could, if you get a bad joint somewhere between two sections then every circuit will loose its earth path. So for instance i have over 300 circuits
 
"And the drops from trunking to sockets are in plastic conduit with only one cpc in" from that statement it reads that each plastic trunking has 1 x cpc (if this was 1 x leg returning to the DB the conduits except the last socket on the ring would have 2 x cpc 1 in 1 out etc " so if only 1 x cpc in each drop what does that indicate to you .................
 
I have continuity on line to line and neutral to neutral and all on 32amp mcbs labelled as rings
 

Reply to Eicr coding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
397
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

It’s difficult to advise on an electrical issue when some isn’t very conversant with electrical terminology.
Replies
14
Views
1K
Agree when you have a Senior Moment how is that still allowed, especially with all the regulations in place now, always a dangerous situation in...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top