bristolsparky
Hi Chaps,
Sorry its late but im after some advice from some maybe wiser men....
I have carried out a EICR on a multiple unit trading estate owned by a farmer.
I have discovered that nearly all the 3 phase DB'd are corroded and have asbestos flash guards with bs3036 fuses. I have put the fuses down as limitation in my report as i did not want to disturb them etc. I have also explained to the landlord that i recommend that the 3 phase DB's are to be replaced....
I have given him costs and time schedule etc of which he honestly explained he cannot afford the costs involved but wants to try and think of another cost effective way to repair the defects identified. I have explained that DB's in question have a fair amount of corrosion and advise to replace them.
His reponse was to get a asbestos company in to remove all asbestos in the distribution boards and that would be it?!??!! I explained that they are still very corroded and very old. All the ZS results etc are fine and earthing is acceptable but i am not happy signing my name away without replacing the db's but would like to help him out and gain future work with him....
Please see pics of the defects i have found mainly the rusty DB's TPN
Any advice on how to proceed? I personally think the only option is to replace them....
Sorry its late but im after some advice from some maybe wiser men....
I have carried out a EICR on a multiple unit trading estate owned by a farmer.
I have discovered that nearly all the 3 phase DB'd are corroded and have asbestos flash guards with bs3036 fuses. I have put the fuses down as limitation in my report as i did not want to disturb them etc. I have also explained to the landlord that i recommend that the 3 phase DB's are to be replaced....
I have given him costs and time schedule etc of which he honestly explained he cannot afford the costs involved but wants to try and think of another cost effective way to repair the defects identified. I have explained that DB's in question have a fair amount of corrosion and advise to replace them.
His reponse was to get a asbestos company in to remove all asbestos in the distribution boards and that would be it?!??!! I explained that they are still very corroded and very old. All the ZS results etc are fine and earthing is acceptable but i am not happy signing my name away without replacing the db's but would like to help him out and gain future work with him....
Please see pics of the defects i have found mainly the rusty DB's TPN
Any advice on how to proceed? I personally think the only option is to replace them....