EICR done in 2 stages? | on ElectriciansForums

Discuss EICR done in 2 stages? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

surfmk

DIY
Joined
Jan 5, 2023
Messages
10
Reaction score
5
Location
Brighton
Hi all,

Does anyone know if I can pay to have an EICR done for part of a house (so I can put plasterboard up etc... safe in the knowledge that that section of the house is OK?). I'm doing quite a large building project on 5 bedroom house.

Could I do the remaining part (kitchen) on a separate occasion? Would a failed EIRC - or loads of C3s be a permanent record on a property if for example the electrician insisted on checking the whole house? I don't mind paying for 2 EIRC but don't want to start taking down plasterboard!

Many thanks

Paul.
 
An EICR can cover whatever part of the property you wish - this can be stated in the Extent covered by the report, and the Limitations.

For example, I have carried out EICRs on part of a house, where that part is let out. So it includes the circuits in that part, but does also include the relevant distribution board / consumer unit where ever that is.

Where is gets difficult is if a circuit is partly in the rooms you want to cover, and partly in the rooms you don't want to cover. But then for example, a limitation might be that certain outlets or lighting points on a circuit are excluded - which is all very well if the circuit otherwise tests good, but if there are deficiences on the circuit to find, they could be in excluded part.
 
Hi all,

Does anyone know if I can pay to have an EICR done for part of a house (so I can put plasterboard up etc... safe in the knowledge that that section of the house is OK?). I'm doing quite a large building project on 5 bedroom house.

Could I do the remaining part (kitchen) on a separate occasion? Would a failed EIRC - or loads of C3s be a permanent record on a property if for example the electrician insisted on checking the whole house? I don't mind paying for 2 EIRC but don't want to start taking down plasterboard!

Many thanks

Paul.

Assuming those are new circuits going in, presumably whoever's fitting them will test the cables as installs are completed to spot any early faults? That should give you some assurance they're OK before finishing the rooms but the completed installation will need to be re-tested when everything's done to pick up any issues caused during the rest of the work... snagged cables, screws through wires, loose connections etc.
 
If new circuits they should be certified on an EIC (with LA notification). not an EICR

You can have an EICR done on any 'existing' installation or part thereof from a single circuit to the whole installation.
 
The Idea is the EICR to be done on the whole system, re: the circuits. Are you doing the circuits your self?
Thanks for the reply, yes I have extended a number of circuits and Building Control asked me for an EICR when the project is finished (which was a full planning job). My problem is that I need to start putting plasterboard back and although the wiring is completed upstairs, the kitchen has not been touched as yet. So in an ideal world, I would ask an electrician to do an EICR on the 80% that is complete and then do the kitchen in a month or 2 and then hand the report to BC.

The grey area for me is bonding as the whole central heating system is copper (completely replaced) and the incoming water main is PDME and Gas is copper. So I have made sure we have 10mm bonding on both Gas and water (although as every circuit is RCBO protected I might not have needed the water bonded).

I just didn't want to be told that I need supplemental bonding etc.. later when access would be really difficult (easy now).

Thanks again for your time.
 
An EICR can cover whatever part of the property you wish - this can be stated in the Extent covered by the report, and the Limitations.

For example, I have carried out EICRs on part of a house, where that part is let out. So it includes the circuits in that part, but does also include the relevant distribution board / consumer unit where ever that is.

Where is gets difficult is if a circuit is partly in the rooms you want to cover, and partly in the rooms you don't want to cover. But then for example, a limitation might be that certain outlets or lighting points on a circuit are excluded - which is all very well if the circuit otherwise tests good, but if there are deficiences on the circuit to find, they could be in excluded part.
Hi SJD,

This is exactly what I needed to understand, so thanks for your explanation.

If new circuits they should be certified on an EIC (with LA notification). not an EICR

You can have an EICR done on any 'existing' installation or part thereof from a single circuit to the whole installation.
I have spoken to the head of Building Control - Brighton regarding this and the LA notification on new circuits fall under the whole LA notifiable works (of which there are many) on this project. As a result I need to have condition report(s) from a Part P certified electrician to confirm any new circuits have been completed to the required standard. So the best way I can see of doing this is to request an EICR where new circuits are highlighted and accessible (in the kitchen this is yet to happen). The condition report will become a part of the entire notifiable works on the project even though no Part P certificate has been issued.

I questioned head of Building Control (Mike Sansom) about the lack of Part P certificate as follows and his reply follows below:

In that case, if I were to employ an electrician to do a detailed condition report (but not provide a full Part P certificate) would this satisfy your requirements and be in keeping with building regulations?

Yes. The key for me is that the wiring is installed as it should be, the necessary safety features are in place and that an independent competent electrician has tested and checked the installation for safety.
 
Entirely new circuits require an Electrical Installation Certificate not an EICR and require notification. Alterations require Minor Works Certificates not an EICR and depending on where they have been altered may well not require notification
 
I think the OP is doing the electrical work himself (as said in #2), and has been open with that to his LBC?

The LBC, as normal, do not know how to deal with this, and have suggested an EICR, which will allow a final Competition Certificate to be supplied by them, when the whole project is finished, which will incorporate the electrical installation?
 
Entirely new circuits require an Electrical Installation Certificate not an EICR and require notification. Alterations require Minor Works Certificates not an EICR and depending on where they have been altered may well not require notification
I understand this is true if I didn't already have notifiable building works (which includes electrical work) being carried out at the property. I have been instructed to get an EICR from Building Control to support my documentation. They are however using this in conjunction with regular inspections which check installation locations / cable protection regulations etc...are all met.

Please see my Q&A below:

-----------------
Q: My concern is that if someone asked for certificates in future I would only be able to produce a condition report… but maybe this is all I need?

A: You would refer to the information you provided to Building Control (condition report) in order to have the work signed off. If we issue a completion certificate that includes the electrical work then you will be ok. It is not uncommon for people selling their house not to have a Part P certificate from a competent person.
-----------------

(I highlighted the critical but in italics). So, this is why my original question was... "can I get a condition report on part of an installation?". I have been asked to produce this by BC and I'd like to do this while the wiring is still accessible.
 
I think the OP is doing the electrical work himself (as said in #2), and has been open with that to his LBC?

The LBC, as normal, do not know how to deal with this, and have suggested an EICR, which will allow a final Competition Certificate to be supplied by them, when the whole project is finished, which will incorporate the electrical installation?

Not a slight against the OP, whose work I'll assume is excellent, but this highlights the farcical nature of 'Part P regulations' when local authorities provide a means of bypassing requirements that electrical contractors are obligated to abide by.
 
I think the OP is doing the electrical work himself (as said in #2), and has been open with that to his LBC?

The LBC, as normal, do not know how to deal with this, and have suggested an EICR, which will allow a final Competition Certificate to be supplied by them, when the whole project is finished, which will incorporate the electrical installation?
Yes I have been completely open with LBC and yes the final Competition Certificate does incorporate the electrical installation.
You have been a lot more efficient in your wording than I was. They need proof between their own inspectors and qualified electricians that the electrical installation is safe (but no EIC). The head of BC said (over the phone) that it was up to them how these requirements were met.
 
Not a slight against the OP, whose work I'll assume is excellent, but this highlights the farcical nature of 'Part P regulations' when local authorities provide a means of bypassing requirements that electrical contractors are obligated to abide by.
I understand your point... my work is to a very high standard (electronics / mechanical engineering etc...) and I have a Site Guide but it does seem to bypass it as you say.
 
Not a slight against the OP, whose work I'll assume is excellent, but this highlights the farcical nature of 'Part P regulations' when local authorities provide a means of bypassing requirements that electrical contractors are obligated to abide by.
Yes it does seem nonsensical.

I think the whole drive for regulating who should carry out electrical work, via Part P, was to stop untrained & unqualified people carrying out electrical work, in domestic properties. You don't see or hear many 'YouTube' trained companies working in the commercial or industrial market place.

Our OP's thread has proved aspects of Part P have not worked, no offence to OP.

Its the drive some people have to save money, is where we are. I hear same people say they can't trust traders to do their work, and are only confident in themselves carrying out the work. Poor state of affairs, where we can't legislate about poor trades people and those who what to save money, perhaps to the detriment of others.
 

Reply to EICR done in 2 stages? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
676
Heh I know the brochures for courses with stock images of women using tools in random scenarios but when you're there it never happens, it's all...
    • Like
Replies
2
Views
331

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top