Discuss EICR downgraded by Landlord’s Agent from C2 to C3 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
No they don't. They just manage the properties on behalf of the landlord who has several thousand.Do they own it.
No they don't. They just manage the properties on behalf of the landlord who has several thousand.
You are probably correct in that assumption but unfortunately it is a Code 2 in the Report and the agent does not have the powers to change this. It could also be a 100ma rcd and the individual misread it, does not trip at ×1 on a 30ma test but it will at ×5.Before I say how I think the Agent may be trying to wriggle out of item 11 being a C2 I want to say that I think the C2 items should be addressed and corrected by the agent and that as has been said previously only doing another EICR can result in a different classification.
Obviously if the RCD does not trip at all at its rated current then it is faulty and should be replaced. Do we have any test results for the RCD?
Anyway here is what I think the agent is trying to use to wriggle out of C2 classification:
First I will assume the RCD is only for additional protection. Then referring to Regulation 643.8 "Effectiveness is deemed to have been verified...disconnects within 40mS when tested at a current equal to or higher than five times its rated residual operating current". So if the RCD disconnected within 40mS at 5x its rated current it is deemed to be effective.
I think BPG 4 suggests a C2 for this.Although most of us agree sockets that may feed outside equipment should have RCD protection, it would only be a C3.
“Suggests” a C2 and that’s just a best practice guide.I think BPG 4 suggests a C2 for this.
The regs have required this for nearly 15 years now, much longer than the requirement for domestic lighting circuits to have rcd protection (which bpg 4 suggests is a C3) so the two things aren’t entirely equal in one sense.
Good spot…. I thought it was stuffed with caulk.I would code item 3 a C2 as you should not be able to stick your finger in the top of a consumer unit.
Pesky circuit breakers that keep trippingGood spot…. I thought it was stuffed with caulk.
Strange that the fuse cover has been cut open, as if the fuses were at one time replaced with the push in circuit breakers… but are now back to fuses?