Nobody has said it is unsafe for continued use. It has been deemed unsatisfactory.

Unsafe and unsatisfactory mean different things.
Oh I see

Ok, Lets pretend. I am the customer you are the electrician.

I need an EICR and I am requesting the report and paying for the inspection. Any relevant questions at this stage you as the electrician would ask. (Extent perhaps - sayin')

6 circuits in the board and out of the 6 you tell me only 4 have been inspected because 2 you could not trace.

Turning to my EICR based on model form which you have completed.
Page 1 lets fill this part in:

'Overall assessment of the installation in terms of its suitability for continued use - SATISFACTORY / UNSATISFACTORY (delete as appropriate)'

What are you going to delete?

Turning to the observations and coding. I see the two circuits you have not identified are coded F. I.
I read the notes and see these are issues that require further investigation WITHOUT DELAY (caps mine).
Sounds serious so I read the notes on the EICR and now ask you a few questions
"Why should these circuits be traced WITHOUT DELAY ?" " I see it says they could be potentially dangerous, what makes you believe they are potentially dangerous?"

I need a SATISFACTORY finding on the EICR (Extent - whats that then) so you agree to come back a second time to trace the circuits you have not traced this time. For a fee (obviously).
Do you start ripping up my new floors, cut holes in my decorated walls and take down sections of ceiling to find these two pesky cables?
 
Last edited:
Oh I see

Ok, Lets pretend. I am the customer you are the electrician.

I need an EICR and I am requesting the report and paying for the inspection. Any relevant questions at this stage you as the electrician would ask. (Extent perhaps - sayin')

6 circuits in the board and out of the 6 you tell me only 4 have been inspected because 2 you could not trace.

Turning to my EICR based on model form which you have completed.
Page 1 lets fill this part in:

'Overall assessment of the installation in terms of its suitability for continued use - SATISFACTORY / UNSATISFACTORY (delete as appropriate)'

What are you going to delete?

Turning to the observations and coding. I see the two circuits you have not identified are coded F. I.
I read the notes and see these are issues that require further investigation WITHOUT DELAY (caps mine).
Sounds serious so I read the notes on the EICR and now ask you a few questions
"Why should these circuits be traced WITHOUT DELAY ?" " I see it says they could be potentially dangerous, what makes you believe they are potentially dangerous?"

I need a SATISFACTORY finding on the EICR (Extent - whats that then) so you agree to come back a second time to trace the circuits you have not traced this time. For a fee (obviously).
Do you start ripping up my new floors, cut holes in my decorated walls and take down sections of ceiling to find these two pesky cables?
Figuring out you can't trace them is PART OF THE EICR. You're basically saying the whole notion of an FI is wrong. Which makes you wrong, sorry.
 
Normally I would use the Electrical Safety First Guidance Note 4 for industry-backed guidance on EICR coding issues.
However, in this instance, there is conflicting guidance between the latest guidance and the previous guidance when it comes to FI codes. This is not at all helpful!

In BPG4 Issue 5 it clearly states that circuits that are not identified and not readily traced would warrant an FI.

Then you get this, directly copied from BPG4 Issue 6:

"FI - Further investigation required without delay.
In a domestic or similar installation, it should
generally be possible to attribute a Classification Code to each observation without the need for further investigation.
No examples of FI codes applicable for domestic and similar installations are given in this guide.
The purpose of periodic inspection, as previously stated, is not to carry out a fault-finding exercise, but to assess and report on the condition of an installation within the agreed extent and limitations of the inspection. Therefore, where an observation can be attributed a Classification Code, further investigation would not be required for the purposes of completing the condition report.
Further investigation should be called for in respect of any observation that could reasonably be expected to reveal danger or potential danger.
Further investigation should not be called for simply because it would be ‘nice to know' – for example, why a socket-outlet is unearthed.
If an observation cannot be attributed a
Classification Code due to reasonable doubt as to whether danger or potential danger exists, the outcome of the assessment must be reported to be unsatisfactory.
The person ordering the report should be advised that the inspection and/or testing has revealed a potential safety issue which could not, due to the agreed extent or limitations of the inspection, be fully determined, and that the issue should be investigated as soon as possible."
 
Normally I would use the Electrical Safety First Guidance Note 4 for industry-backed guidance on EICR coding issues.
However, in this instance, there is conflicting guidance between the latest guidance and the previous guidance when it comes to FI codes. This is not at all helpful!

In BPG4 Issue 5 it clearly states that circuits that are not identified and not readily traced would warrant an FI.

Then you get this, directly copied from BPG4 Issue 6:

"FI - Further investigation required without delay.
In a domestic or similar installation, it should
generally be possible to attribute a Classification Code to each observation without the need for further investigation.
No examples of FI codes applicable for domestic and similar installations are given in this guide.
The purpose of periodic inspection, as previously stated, is not to carry out a fault-finding exercise, but to assess and report on the condition of an installation within the agreed extent and limitations of the inspection. Therefore, where an observation can be attributed a Classification Code, further investigation would not be required for the purposes of completing the condition report.
Further investigation should be called for in respect of any observation that could reasonably be expected to reveal danger or potential danger.
Further investigation should not be called for simply because it would be ‘nice to know' – for example, why a socket-outlet is unearthed.
If an observation cannot be attributed a
Classification Code due to reasonable doubt as to whether danger or potential danger exists, the outcome of the assessment must be reported to be unsatisfactory.
The person ordering the report should be advised that the inspection and/or testing has revealed a potential safety issue which could not, due to the agreed extent or limitations of the inspection, be fully determined, and that the issue should be investigated as soon as possible."
I don't see the conflict there.
 
I don't see the conflict there.
No? There's at least an omission from the previous issue. That is, the previous issue stated directly that an untraced circuit should be give an FI code. The current issue states that no examples are given of what would warrant an FI code.
 
No? There's at least an omission from the previous issue. That is, the previous issue stated directly that an untraced circuit should be give an FI code. The current issue states that no examples are given of what would warrant an FI code.
'Therefore, where an observation can be attributed a Classification Code, further investigation would not be required for the purposes of completing the condition report.'

You can't code what you can't see therefore FI required.
 
Seeing as I am unable to post in any other thread but this let me end my time here.

Quote:
'You can't code what you can't see therefore FI required.'

Is F.I. not a coding then?

-------

As I have already said; you can't trace a circuit on this EICR thats you are charging the client for. Thus you decide to require a 'Further Investigation' take place at some later point in time and note on the EICR paperwork an F. I. coding.
Tell me, what are you going to do different on those follow up visits to trace the circuits that you could not do on that initial visit?

Oh never mind. Let me end with a regulation.
651.1 (later part). On an EICR you have unknown circuit / circuits as such it would be reasonable to say in this scenario that you have no existing documentation to identify such circuits. Prior to carrying out the EICR what should you do ?

The electrical industry is aiming for the bottom
 
Seeing as I am unable to post in any other thread but this let me end my time here.

Quote:
'You can't code what you can't see therefore FI required.'

Is F.I. not a coding then?
Call it whatever you like; but it means the EICR is unsatisfactory.
-------

As I have already said; you can't trace a circuit on this EICR thats you are charging the client for. Thus you decide to require a 'Further Investigation' take place at some later point in time and note on the EICR paperwork an F. I. coding.
FI is a perfectly reasonable PART OF AN EICR.
Tell me, what are you going to do different on those follow up visits to trace the circuits that you could not do on that initial visit?
Trace them. And get appropriately paid for doing so.
 
Last edited by a moderator:

Reply to EICR FI faults holding up Satisfactory certificate. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top