I have been to 2 different rental properties this week, one for an EICR and the other for a report of the smell of fish from the shower isolator when the shower was in use.

As part of the EICR, I removed the shower cover to measure R1+R2 and Zs at the shower and a general inspection, only to discover a loose connection and a badly damaged terminal block in the shower which had overheated. Also at the same property in same shower, a loose connection had melted the back of the isolation pull cord so the isolator was stuck permanently on. Both rectified and put back into service.

At the fish smelling isolator, it was a wall mounted 45A DP isolator with neon outside the bathroom. Same again, loose connection, melting the cable insulation and back of the switch.

Being rental properties I hoped to get hold of the previous EICR's but I had no access to them for one reason or another, but I did wonder if anyone had ever checked these items before. In both cases the cables were so loose in their connectors I question whether they had ever been tightened and also whether they had ever been checked.

[ElectriciansForums.net] EICR - How much do you check?


[ElectriciansForums.net] EICR - How much do you check?
 
Its usually a progressive exercise,find problems and look deeper for more
Having said that,shower circuit connections are notorious for being poor and they need inspecting as routine.


Looking at the effort that was made in those pictures,I would be on my best rip the installation to bits behaviour
 
Its usually a progressive exercise,find problems and look deeper for more
Having said that,shower circuit connections are notorious for being poor and they need inspecting as routine.


Looking at the effort that was made in those pictures,I would be on my best rip the installation to bits behaviour
I did - It wasn't hard though, most of it was staring me in the face without digging deep. It's a real mess.
 
don't let IET see those pics. the 18th will have an amendment within 12 months , calling for all showers to be housed in non-combustible enclosures.

Lol I'm imagining a galvanised cubicle with wired glass door. Swmbo would have a fit. Could always fit a sprinkler as well, just to be on the safe side. Maybe the sprinkler could then be used as the shower. Hang on ! It's a "there's a hole in my bucket" moment.
 

Reply to EICR - How much do you check? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
401
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
989
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
270
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top