Still code 2 for me,it’s definitely not correct ,still needs a enclosure,pattresss.What code do you think something that complies with the regulations attracts?
If unsheathed cables were visible outside the enclosure once on I'd agree C2, but for the sake of argument is this any different from most of the metal decorative light fittings that come with a single bar that connects to the ceiling - they have no 'back' other than that provided by the plasterboard, yet the cabling within is usually not sheathed or in a separate enclosure (apart from the IP rated ones which are those hideous tiny ones)Still code 2 for me,it’s definitely not correct ,still needs a enclosure,pattresss.
Rough perhaps, but I think it may be okay, and compliant. Here is why:
526.5
Every termination and joint in a live conductor or a PEN conductor shall be made within one of the following or a combination thereof:
(i) A suitable accessory complying with the appropriate product standard
(ii) An equipment enclosure complying with the appropriate product standard
(iii) An enclosure partially formed or completed with building material which is non-combustible when tested to BS 476-4.
I know precisely nothing about BS 476-4, but I find it difficult to imagine that brickwork, plaster, plasterboard etc would be deemed combustible when tested to any standard.
What’s your thoughts on this,codes etc.
Quite a lot if these,on wall lights & chain hanging lanterns.
It needs some enclosure sure, but it was ok 20 years ago,& no probs.
C2 - potentially dangerous. How so?Still code 2 for me,it’s definitely not correct ,still needs a enclosure,pattresss.
These are ok, but I always worry that I might accidentally release the conductors when cramming them into whatever is enclosing them. I prefer the lever 221s myself.The Wago 224 are ideal for this sort of thing. Used some in similar situation where there was barely any earth left (had been cut short) though in this case there was a metal architrave box or similar in the wall.
These are ok, but I always worry that I might accidentally release the conductors when cramming them into whatever is enclosing them. I prefer the lever 221s myself.
If the wall light is a metallic class 2 one, then I'd agree, the terminations would need to be in one of those supplied tiny plastic boxes to insulated them from the metal casing. But looking at your picture it appears to be earthed, so I'm assuming class 1? In which case I don't see any problem with the connections being made in the base (again I'm assuming a hollow metallic base).all cabling needs to be connected in appropriate enclosure,the wall light is not an enclosure.
Single insulated cable outside of an enclosure, according to NAPIT codebreakers its a C2 and I totally agree.
Almost certainly. Many light fittings with a hollow base have a connector block fixed in their base, the centre terminal connected to a tab earthing the fitting. Where else are you going to make the connection?would the light fitting itself form an enclosure thou ...?
The three paragraphs you have selected from BPG4 wouldn't apply in the case of your original post because:Code 2,says it all really.
[automerge]1601191955[/automerge]
Another one bites the dust ?
Could be potentially dangerous,& definitely a fire hazard.The three paragraphs you have selected from BPG4 wouldn't apply in the case of your original post because:
1. Single insulated conductors are not accessible to touch or likely to come into contact with metalwork
2. Connections are made within an enclosure according to BS7671. Read carefully the regulation I posted at #11
3. No fire barrier has been breached
With this in mind, please explain how you think this is a C2 - potentially dangerous?