Tabulated values (table 4D2A) are 16.5A for ref method B and 19.5A for ref method C
Minimum permitted cable size for a power circuit is 1.5mm

So assuming there are no de-rating factors to be applied then I don’t see any reason to record it as an observation on an EICR.

I had someone try to code a similar circuit I had installed a little while ago, 16A RCBO feeding a twin socket via 2 metres of 1.5mm SWA clipped direct. Thankfully the customer was on the ball and produced the installation certificate and suggested they phone me if they needed clarification, so the numpty gave up on that one.
Not sure but does FP 200 fall under this category??
 
Tabulated values (table 4D2A) are 16.5A for ref method B and 19.5A for ref method C
Minimum permitted cable size for a power circuit is 1.5mm

So assuming there are no de-rating factors to be applied then I don’t see any reason to record it as an observation on an EICR.

I had someone try to code a similar circuit I had installed a little while ago, 16A RCBO feeding a twin socket via 2 metres of 1.5mm SWA clipped direct. Thankfully the customer was on the ball and produced the installation certificate and suggested they phone me if they needed clarification, so the numpty gave up on that one.
Not sure but does FP 200 fall under this category??
 

Reply to EICR : Is this a code 2 or not? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
460
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
949
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
895

Similar threads

Agree when you have a Senior Moment how is that still allowed, especially with all the regulations in place now, always a dangerous situation in...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top