Hey all,
Been to do an EICR on an oldish property before rental plus add in some sockets in garage etc..
Problems mostly been sorted while doing the new sockets etc.. but have no r1,rn or r2 on what I presume is supposed to be a ring final covering the entire house. I haven't gone any further with the diagnosis on this circuit as yet due to the estimate for sorting will need to go through the relatives lawyers apparently ! possibly a curator situation as I think the rental cash is to go to a care home :-(
Tested Zs and the reading is way too high anyway as is at 1.67 ohms on an old Wylex 60898 mcb, two blade type B that fits in old BS3036 CU / 3kA ones. Hoping just a sketchy old socket or loose termination but has green goo issue too !
Anyone think loose connection could explain the higher Zs ? found a few spurs run surface etc.. but whole house should be under 100M² anyway as quite a small bungalow.
Been to do an EICR on an oldish property before rental plus add in some sockets in garage etc..
Problems mostly been sorted while doing the new sockets etc.. but have no r1,rn or r2 on what I presume is supposed to be a ring final covering the entire house. I haven't gone any further with the diagnosis on this circuit as yet due to the estimate for sorting will need to go through the relatives lawyers apparently ! possibly a curator situation as I think the rental cash is to go to a care home :-(
Tested Zs and the reading is way too high anyway as is at 1.67 ohms on an old Wylex 60898 mcb, two blade type B that fits in old BS3036 CU / 3kA ones. Hoping just a sketchy old socket or loose termination but has green goo issue too !
Anyone think loose connection could explain the higher Zs ? found a few spurs run surface etc.. but whole house should be under 100M² anyway as quite a small bungalow.