I have been doing EICR's for many years but for the first time today, I was unable to locate the mains water stopcock. The property is a flat in Chelsea and its recently been renovated (worth a few quid). I searched all the usual places but didn't want to start tearing apart their kitchen and removing their professionally fitted appliances, not to mention the well painted/ tiled boxing in both bathrooms.I know even if it is bonded at all, it's only 6mm from the cables at the MET and CU.
It was for a letting agent so had finish the report today, but feel that it's inadequate to just state it as a limitation.
What would u guys do, shall I go back an have another look or, just note it?
Have u ever been in this situation?
Cheers
Steve.
If you have a 6mm cable from the MET to some unknown location and the resistance from that cable to the water pipe is low then I would note the inaccessible unchecked water bonding connection as a limitation and the resistance reading.
Best to find it if you can, they will probably need to turn the water off at some point and would want to know where the stop cock is located!
Had this situation many a time. What i usually do is isolate the supply, disconnect all the 6mm2 earthing cables or 10mm2 whatever they may be. Do a continuity wander lead test between water pipe under kitchen sink or accessible water pipe location and each cable at m.e.t / board bar.Record the reading and confirm ohmic value. Label the cable with the lowest reading as 'suspected inaccessible o2 bond' make a note in the limitations box on your cert and advise further investigation subject to client agreement. Job done!
If there is no sign of separate 6 or 10mm2 cables then it is safe to say there is no means of adequate bonding ( if the pipework is not plastic of course)
Took my assessor to a job I had done 3 months prior. Board change and large extension etc.
I knew exactly where the stop cock was, only to find it had been plaster boarded and plastered over, no access whatsoever to use the stopcock !!
Luckily there was a pipe coming out of the new wall that I could demonstrate connection from. The customer was a little surprised too !!!
Reply to EICR issues! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...