These are my EICR limitations please can I have your opinion of these and any suggestions of any additional ones
1. As a minimum, 30% of electrical accessories will be visually inspected unless prevented( I.e. Artex ceiling)
2. Zs values inputted will be calculated except socket circuits in order to minimise live working.
3. Loft spaces will not be accessed due the the risk of workin at height unless required to access electrical equipment.
4.DNO fuse I formation not obtained, after attempting to enquire.
5. Intruder alarm system wiring not tested.
6. Central heating wiring and controls not tested however cpc verified at each point.
7. Live to neutral insulation testing omitted in order to minimise risk of damaging equipment,
8. Where a gas cooker is installed within a property the cooker circuit will be tested to the point of insulation only if access to an outlet is prevented by the appliance. This is to eradicate the need to disturb any has appliance.
9. Where a circuit supplies integrate appliance test will be undertaken to the point of isolation only to minimise/ eradicate the risk of damaging equipment.
10. Where a manual handling risk is identified, (ie large kitchen appliance) testing will be undertaken at the point of isolation or where this is not possible will be omitted and listed as an operation limitation.
11. No pat testing of items with a 13amp plug top( note cooker etc should have a minimum of r2 continuity test.
12.on an off peak supply the Zs results will be calculated using the 24h supply Ze.
13. On a circuit with a storage heater the test will be carried out at the point of isolation and r2 continuity verified at the storage heater.
1. As a minimum, 30% of electrical accessories will be visually inspected unless prevented( I.e. Artex ceiling)
2. Zs values inputted will be calculated except socket circuits in order to minimise live working.
3. Loft spaces will not be accessed due the the risk of workin at height unless required to access electrical equipment.
4.DNO fuse I formation not obtained, after attempting to enquire.
5. Intruder alarm system wiring not tested.
6. Central heating wiring and controls not tested however cpc verified at each point.
7. Live to neutral insulation testing omitted in order to minimise risk of damaging equipment,
8. Where a gas cooker is installed within a property the cooker circuit will be tested to the point of insulation only if access to an outlet is prevented by the appliance. This is to eradicate the need to disturb any has appliance.
9. Where a circuit supplies integrate appliance test will be undertaken to the point of isolation only to minimise/ eradicate the risk of damaging equipment.
10. Where a manual handling risk is identified, (ie large kitchen appliance) testing will be undertaken at the point of isolation or where this is not possible will be omitted and listed as an operation limitation.
11. No pat testing of items with a 13amp plug top( note cooker etc should have a minimum of r2 continuity test.
12.on an off peak supply the Zs results will be calculated using the 24h supply Ze.
13. On a circuit with a storage heater the test will be carried out at the point of isolation and r2 continuity verified at the storage heater.