All - Would appreciate some advise or professional help as I'm facing a £4.5K bill following an EICR which seems to highlight issues that passed just last year's EICR.
First EICR done in March 2021 - Passed with only C3 observations.
Second EICR done - just on advise online before change of tenancy - Failed with multiple C2. The tenancts are due in by end of Month and we are facing a hefty bill. Focus of course is to make it safe for tenants but don't want to be ripped off hence would appreciate some advise or professional help.
1 1.3 Consumer meter tails exposed single insulated inner cores. C2 Meter [March 2021 none highlighted]
2 . No labels on Earthing Conductor and Main Earthing Terminal. C3 MET
3 4.1 Consumer unit mounted at a height which prevents ease of access for user. C3 Entrance [March 2021 No observation see pic under next point[]
4 4.5 IP rating of consumer unit not to BS 7671:2018+A2:2022. Back and top of Consumer unit has an unused opening exceeding IP2X. C2 Consumer unit [March 2021 reading marked as pass. New Consumer Board was installed 2012/13 when we upgraded the kitchen]
5 4.6 Consumer unit in a domestic household premises is not metal, located in the sole means of escape for a dwelling area. C2 Entrance [March 2021 no issue highlighted]
6 4.7 Consumer unit has a crack in the protective device access flap. C2 Consumer unit [March 2021 this was a C3]
7 4.17 No presence of diagram, charts at or near equipment. C3 Consumer unit
8 6.3 Low values of insulation resistance measured 250V DC test voltage (2.28M/ohm). Degraded di-isoctyl phthalate occurying in all checked sockets (except kitchen circuit) wires and sockets throughout the house. C2 Several locations [March 2021 reading >200MOHM]
9 6.14Mains smoke/heat alarms not installed. Battery alarms poor condition. Advise install minimum 10 years Mains with battery back-up smoke/heat alarms. C3 Several locations [March 2021 not highighted]
Thanks!!!
J
First EICR done in March 2021 - Passed with only C3 observations.
Second EICR done - just on advise online before change of tenancy - Failed with multiple C2. The tenancts are due in by end of Month and we are facing a hefty bill. Focus of course is to make it safe for tenants but don't want to be ripped off hence would appreciate some advise or professional help.
1 1.3 Consumer meter tails exposed single insulated inner cores. C2 Meter [March 2021 none highlighted]
2 . No labels on Earthing Conductor and Main Earthing Terminal. C3 MET
3 4.1 Consumer unit mounted at a height which prevents ease of access for user. C3 Entrance [March 2021 No observation see pic under next point[]
4 4.5 IP rating of consumer unit not to BS 7671:2018+A2:2022. Back and top of Consumer unit has an unused opening exceeding IP2X. C2 Consumer unit [March 2021 reading marked as pass. New Consumer Board was installed 2012/13 when we upgraded the kitchen]
5 4.6 Consumer unit in a domestic household premises is not metal, located in the sole means of escape for a dwelling area. C2 Entrance [March 2021 no issue highlighted]
6 4.7 Consumer unit has a crack in the protective device access flap. C2 Consumer unit [March 2021 this was a C3]
7 4.17 No presence of diagram, charts at or near equipment. C3 Consumer unit
8 6.3 Low values of insulation resistance measured 250V DC test voltage (2.28M/ohm). Degraded di-isoctyl phthalate occurying in all checked sockets (except kitchen circuit) wires and sockets throughout the house. C2 Several locations [March 2021 reading >200MOHM]
9 6.14Mains smoke/heat alarms not installed. Battery alarms poor condition. Advise install minimum 10 years Mains with battery back-up smoke/heat alarms. C3 Several locations [March 2021 not highighted]
Thanks!!!