As for the C2 given for the plastic consumer unit being located in the sole means of escape, BPG4 would suggest this would be C2 only if there were signs of degradation in the consumer unit. For example, discolouration of MCBs, badly fitted busbars etc.

Having said that, there is an obvious benefit to keeping up with current regulations that are designed to improve safety.
 
It might be worth thinking about getting all the other circuits rewired at the same time if they are of a similar age, or at least discuss it with the electrician.
To be fair I can see at least 3 circuits in new colours, so I'm expecting this to be a partial rewire.

What I would say is that getting this done while unoccupied will save big bucks.
 
To be fair I can see at least 3 circuits in new colours, so I'm expecting this to be a partial rewire.

What I would say is that getting this done while unoccupied will save big bucks.
Haha.. I just saw this and edited my post. Not quickly enough though 😀
 
The meter tails are at the meter. Can only be worked on by meter operator engineer, as it means pulling the fuse/ cutting the seal

The holes in the consumer unit are up against the ceiling… jam a bit of plastic inbetween to cover.😄

Should get a replacement cover off eBay… at least it’s still got a cover!

The green goo is the biggest issue, but the low readings may be linked to that. If the stained sockets were changed, the reading might rise… but the goo would likely start oozing into the new ones…..



This is a problem everywhere when one EICR picks up on thing that another didn’t.
Was it the same company that did both reports?
If not, was there a big difference in price/ time doing the testing?
Different company.
 
I’d question your first electricians approach not your second, although harsh in some areas at least he’s actually looked at the installation….
First one drove by , sucked his teeth , muttered under his breath 'ah looks okay from here'
 

Reply to EICR Nightmare and Advise in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

This fella puts his face to it about halfway through, he has an opinion on the very subject.
Replies
42
Views
4K

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top