Just want to see what people’s thoughts are on this, doing an EICR today. Testing the lighting circuit, 1 cable at every accessory which means joint box somewhere. Hall light is a pendant wired in 2 core PVC cable, no earth at it. Tested at kitchen light and got a reading, then tested at living room light and although cpcs were connected at light and switch I wasn’t getting a reading. I’ve marked this down as further investigating on the lighting circuit, client not too happy that the floorboards are going to have to come up from upstairs lol! Would you pass the circuit in these circumstances? Feel a bit uneasy about it
 
it's a C3 if all fittings are plastic. C2 if metal. your approach is correct to investigate and rectify. serves 'em right for gatting a cheap cowboy in the first place.
 
i would be torn between C3 and C2 even with all plastic fittings. still got metal back boxes on switches with metal faceplate screws. so more inclined to C2.
 
If there's no cpc present, the wire pre dates the requirement for a cpc to be present, and there's no exposed metalwork present, then C3.
If there's a cpc present, with no continuity to the main earth terminal, then it's C2, even if there is no exposed metalwork present.
Chances are that it's modifications done in the '70s, when twin cable was no longer available, and the cpc was just ignored, but it could just be a break in the wiring somewhere, giving the possibility of a disconnected cpc coming into contact with a live terminal, or a fault to the cpc at one point exporting that fault to any other floating cpcs.
 

Reply to EICR no CPC at light in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

You are allowed a sampling process, i feel it would be impossible to I&T every point. If the client is prepared to pay for that so be, you can use...
Replies
8
Views
2K
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
Replies
20
Views
1K
Promised a photo…. Remember, this was working…. And they managed to move in without hitting it…
    • Like
Replies
4
Views
287
  • Question
If they got a shock then something cannot have been isolated.
Replies
7
Views
1K
  • Question
...and that it could soon end up costing more than a circuit rewire, a bit of a gamble and you're still left with the old wiring.
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks