https://www.----------------------------/media/2146/bpg1.pdf

Scroll down to page 9, where you will find a complete discussion and recommended course of action for lighting circuits with no CPCs.
 
During my last Stroma assesment about 3 months ago I was presented with this very question to which I answered C3 if all the fittings were class 2. No apparently. It's C2 all day long now as lack of cpc affects the ability of an RCBO to operate effectively. I did question this but assesor was adamant.
 
During my last Stroma assesment about 3 months ago I was presented with this very question to which I answered C3 if all the fittings were class 2. No apparently. It's C2 all day long now as lack of cpc affects the ability of an RCBO to operate effectively. I did question this but assesor was adamant.
I have always said with ADS you cannot rely upon an rcd in the absence of a cpc.
 
During my last Stroma assesment about 3 months ago I was presented with this very question to which I answered C3 if all the fittings were class 2. No apparently. It's C2 all day long now as lack of cpc affects the ability of an RCBO to operate effectively. I did question this but assesor was adamant.
RCBOs do not need a CPC to operate effectively.

Your assessor is disagreeing with the Electrical Safety First best practice guides. The guide on EICR reporting recommends a C3 where there is a lack of CPC in a circuit supplying items of all insulated all class 2 equipment.
He is of course entitled to his own opinion, but it is up to the inspector to decide whether it's C3 or C2.
 
I have always said with ADS you cannot rely upon an rcd in the absence of a cpc.
I agree with you, except to say in this case that you are also relying on the use of all insulated and or Class 2 equipment.
The ideal solution is always to provide a CPC wherever possible. But as a last resort, the best practice guides give helpful advice on how to address the lack of CPCs in lighting circuits.
And there's nothing to stop you or anyone disagreeing with the advice given, and coding it as C2. It's up to you as the inspector.
 
Best Practice Guides are not something I use and Class II protection cannot be used in a dwelling.
Fair comment. As I said it's up to the person signing the EICR to decide.
Interestingly, when I joined the NICEIC EICR register, I had to agree to use the electrical safety first best practice guide 4 when assessing what code to give.[ElectriciansForums.net] Eicr no CPC on lighting circuit
 
Last edited by a moderator:
RCBOs do not need a CPC to operate effectively.

Your assessor is disagreeing with the Electrical Safety First best practice guides. The guide on EICR reporting recommends a C3 where there is a lack of CPC in a circuit supplying items of all insulated all class 2 equipment.
He is of course entitled to his own opinion, but it is up to the inspector to decide whether it's C3 or C2.
NAPIT (and therefore STROMA) have put their name to that guide, so he's disagreeing with his own scheme's guidance
 
Just one further point of clarification:
I have come across this situation (no CPCs to lighting circuits) several times over the last few years.
In each and every case my EICR code given was a C2.
Also, in each and every case, I did my utmost to convince the client that the first and best option is to rewire the circuits.
Then the 2nd best option would be to run a separate CPC to all the points of the circuit (which is probably more problematic than to rewire the circuit).
Then, as an absolute last resort (maybe lack of finances or only just decorated), to change all accessories and lights to all insulated, with a warning notice on the consumer unit. And with a view to having the circuits rewired in the near future.
To be fair, all but one of the clients agreed to the rewiring of the circuits.

Which raises the question, if the client genuinely cannot afford the cost of rewiring the circuit at this time, do you leave them with a potentially dangerous C2 situation? Or do you offer them the last resort suggested by Electrical Safety First? (Whose board members include IET directors and NICEIC technical directors).
Or do you have any other alternative solutions?
 
Which raises the question, if the client genuinely cannot afford the cost of rewiring the circuit at this time, do you leave them with a potentially dangerous C2 situation?
Other than metallic switches, or possibly light fittings above a bath or similar, where it is possible to touch the fitting while being in contact with something at earth potential (radiator, taps, etc) it is hard to see how it would be a C2, which is basically what BPG4 says (quoted below is for C2 rating):
  • Absence of a circuit protective conductor for a lighting circuit supplying items of Class I equipment, or connected to switches having metallic face plates
So I would go with BPG1 and verify there is no current issue with insulation and change the light switch plates to basic plastic ones. But only if it was the only realistic option.

Edited to add: While not directly related, 410.3.9 (iii) has provision for reduced protection for small parts that present a low risk of significant contact or the ability to be gripped, so things like the face plate screws don't really need covering as they are unlikely to allow enough shock current to be dangerous (assume the person is not soaking wet, of course).
 
Last edited:
Other than metallic switches, or possibly light fittings above a bath or similar, where it is possible to touch the fitting while being in contact with something at earth potential (radiator, taps, etc) it is hard to see how it would be a C2, which is basically what BPG4 says (quoted below is for C2 rating):
  • Absence of a circuit protective conductor for a lighting circuit supplying items of Class I equipment, or connected to switches having metallic face plates
So I would go with BPG1 and verify there is no current issue with insulation and change the light switch plates to basic plastic ones. But only if it was the only realistic option.

Edited to add: While not directly related, 410.3.9 (iii) has provision for reduced protection for small parts that present a low risk of significant contact or the ability to be gripped, so things like the face plate screws don't really need covering as they are unlikely to allow enough shock current to be dangerous (assume the person is not soaking wet, of course).
I’m glad you brought the regulation up because people are convinced in changing the fixing screws to nylon or putting caps over the heads, which is a ridiculously waste of time.
 

Reply to Eicr no CPC on lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
355
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
908
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

My latest trick for this....if completely desperate and you have 3 very short cables .... Make a hole big enough for a quickwire to fit through...
Replies
8
Views
790
It’s difficult to advise on an electrical issue when some isn’t very conversant with electrical terminology.
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top