Hi all



Doing an EICR on a commercial unit. Last time done was 2002. No rcd protection whatsoever and plastic board. All circuitry testing out fine, complete ring, c.p.c's present at all lighting points and other appliances. One thing am unsure on is how to code lack of rcd protection on sockets. From any guidance material read for domestic premises this is now advised C2 but C3 in commercial why would this be? I understand if risk assessment and maintenance plan put in place for circuits where loss of data a concern can be applicable but a potential safety hazard is a potential safety hazard surely. The other thing concerns me is on testing bonding to all pipework test results good upto connection but then after all pipes heavily painted and resistances shoot upwards of 2-3 ohms should this be a concern to me? Also there is a non continuous link from one pipe to another in 6mm although reading up to this clamp is good would others have any concerns with this? Thanks
 
Plastic boards are irrelevant for installations outside of domestic. You must use you own judgement for the lack of additional rcd protection for socket outlets and cables in walls without earthed containment not take the word of a guide book. As long as your main protective bonds are sound in their connection, ie not clamped onto a painted section the fact the pipework is painted is probably irrelevant. Your resistance shooting up is probably a poor connection through the paintwork.
 
Plastic boards are irrelevant for installations outside of domestic. You must use you own judgement for the lack of additional rcd protection for socket outlets and cables in walls without earthed containment not take the word of a guide book. As long as your main protective bonds are sound in their connection, ie not clamped onto a painted section the fact the pipework is painted is probably irrelevant. Your resistance shooting up is probably a poor connection through the paintwork.

Thanks Westward always good to get thoughts/experiences of others
 
Think from what you say it sounds like a "satisfactory" for the report. No damage to fittings everything secure tests ok etc. I would say C3 for no rcd and recommend fitting them as "additional protection" What kind of commercial is it though? I mean if it is a car wash I might take a different view.
 
Think from what you say it sounds like a "satisfactory" for the report. No damage to fittings everything secure tests ok etc. I would say C3 for no rcd and recommend fitting them as "additional protection" What kind of commercial is it though? I mean if it is a car wash I might take a different view.

Thanks Vortigern. C3 is what I went with. All circuits in surface mounted trunking. No bathroom areas, just standard office layout. Double insulated fluorescents. Recommended metal clad board an rcd protection atleast covered self there
 
You cannot Code a plastic board in a non domestic installation it does not apply.
I didn't code it Westward but added it as a comment and recommendation. The way I see it is that if plastic boards have been found to not provide great protection in event of fire starting within them, then in commercial this must surely still be applicable. There maybe less likelihood of loss of life but still a hazard nonetheless
 
As far as the plastic board goes what type is it and what is the enviroment it is fitted in?

If it is an IP rated board fitted in a location where that is required then replacing it for metal would likely be making it less safe.
[automerge]1593116965[/automerge]
I didn't code it Westward but added it as a comment and recommendation. The way I see it is that if plastic boards have been found to not provide great protection in event of fire starting within them, then in commercial this must surely still be applicable. There maybe less likelihood of loss of life but still a hazard nonetheless

Non-metal boards are sometimes required in non-domestic situations because of the nature of the enviroment or the nature of the use of the building.
 

Reply to EICR on commercial unit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
321
  • Question
IMO Better to do something about those ignoring regulations first! Current system is like having a speed limit but not enforcing anyone without a...
2
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top