I couldn't sleep at night if I connected 2 rings on one breaker due to bad practice, so as it has been done by others in this house personally I would try to talk the customer into having the job done right myself, not saying it is a must by any means, but there you are, rollocks to the tin hat I'm happy with my views on this so let the games begin :grin:
 
I couldn't sleep at night if I connected 2 rings on one breaker due to bad practice, so as it has been done by others in this house personally I would try to talk the customer into having the job done right myself, not saying it is a must by any means, but there you are, rollocks to the tin hat I'm happy with my views on this so let the games begin :grin:
Agree with you Mike about bad practice but as regards danger then more of a nuisance imo,if 2 rings on a 32A breaker then it's going to potentially be tripping more often due to the potential extra load but its only the same as having one ring for the whole house isn't it? Still rough though and I personally would want to change it,the only way I would and indeed have stuck 2 rings on one breaker was a situation with a failed breaker late at night where the circuit could not be left dead and no other breaker available,but it was replaced first thing next day.
 
Why c2!, no way! As long as the integrity of the circuits are fine and it's not overloading the mcb causing it to open and rcd protected

Just poor workmanship
 
Hehe, was there enough spare ways when the spark wired it, maybe he over estimated the amount of breakers in the board, ive seen so many circuits in boards now its hard to see past simple errors ppl make, usually when i get there its changing time anyway.

Its always easy to say bad practice in iensight, its what you can do to correct the bad practice maybe do as suggested Add a breaker, maybe make one continues ring and change the fuse.

Its also recommended to use 20A for CU now not 32A so maybe look at some suggetion errors here also, its only bad practice when you know it is.
 
Ah , the old bad practice card , always used when you cant actually find any technical evidence that something is wrong. ;-)

C2 = potential to cause accident / injury / fire.

2 circuits into 1suitably rated mcb where there is no risk of overload damage to cable = no code.

inconvienience to householder who has probably learnt to live with it is not a codeable defect.
a mention in the report comments box at most.
 
Ah , the old bad practice card , always used when you cant actually find any technical evidence that something is wrong. ;-)

C2 = potential to cause accident / injury / fire.

2 circuits into 1suitably rated mcb where there is no risk of overload damage to cable = no code.

inconvienience to householder who has probably learnt to live with it is not a codeable defect.
a mention in the report comments box at most.

Yep I'd agree with that!
 
Nothing wrong with an up front RCD, apart from inconvenience.... The 2 ring into a single MCB is basically the same as a single RFC for the whole house, ...i'm sure everyone has seen that situation before. So basically a code 3 at most or/and a report comment....

Not ideal for both situations, but not really codeable either, more as everyone else says, bad practice than anything else!!
 

Reply to eicr -query over classification codes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
  • Question
True. Although I'd hazard a guess that things like woodworm treatment are probably chemically quite similar? Don't know.
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top