EICR RCD 63A exceeded by breaker total code | Page 2 | on ElectriciansForums
Discuss EICR RCD 63A exceeded by breaker total code in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
True Loz but the OP was just adding up the ratings of the MCBs and the boards illustrated both come with MCBs totalling near or over 200a. So it would be impossible to satisfy the regs as being described here.
I take peoples point here but on PIRs I'll still use my judgement to determine whether I think it's okay for a particular installation.
True thanks for pointing out the actual MCB ratings. I didn't look at that detail.
If course it still may comply - the main fuse could be 63 or 60 amps...
Reply to EICR RCD 63A exceeded by breaker total code in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
I would C2 this, cable is not suitable for the environment its installed in, we would C2 a socket for equipment likely to be used outside , cable...