I done it connected 1st then removed them to test just that circuit

Just a thought but are your spare RCD's Brand New?

https://engx.------.org/f/wiring-and-regulations/28594/cause-of-rcd-not-tripping-with-test-switch

The above was posted 3 years ago and they had the same problem turns out all 3 RCDs were faulty

They were second hand parts from a specialised supplier because new parts were not available but you may have the same issue?
 
Just a thought but are your spare RCD's Brand New?


The above was posted 3 years ago and they had the same problem turns out all 3 RCDs were faulty

They were second hand parts from a specialised supplier because new parts were not available but you may have the same issue?
Yeh mate they were brand new, i changed the sockets in the lounge and it started working, strange because everything tested out ok before and after changing sockets
 
Yeh mate they were brand new, i changed the sockets in the lounge and it started working, strange because everything tested out ok before and after changing sockets
Argh....!
We need IR figures, not 'it tests ok'.
Now we're all thinking 'I bet there was a N-E fault. 😅
 

Reply to EICR - RCD Wont trip on test button in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! âš¡ Please note that all EV Chargers and...
Replies
0
Views
204
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
882
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
832

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top