Hi guys, just looking for some advice on a EICR my brothers wife had done on her grandmothers house.
He he asked me to look over the report as he thinks he's being ripped off, which I must admit it does reek of.
Firstly for for example it has a C1 for the distribution board for a blank missing. Cost to rectify ÂŁ30!!!
another couple of things which is sounds fair enough like no earth to lights. And there is a metal light in the living room.
But rather than just note this, the guy has stated it needs an earth run to it.
I had a quick look at this problem and opened a switch and it's wired in conduit, presumably with the Cpc being supplied by the metal conduit.
this wasn't noted on the report, nor a further investigation req. to see if that would be viable for the earth.
If it was okay there would be no need for a separate earth to be run and no need for the big cost also involved to do it. Was requesting ÂŁ160 to earth the lights!
I would (if it was me) also have given the option to simply replace the fittings with class 2 fittings, and a label at the board, at a much reduced cost. They didn't give this option or even mention it.
Another point was was the main bonding, the gas is bonded, but no visible bond to water.
But in the report its ticked as okay, then further on saying it needs doing. But it simply states on the follow on work to "investigate main bonding" with no mention of remedial work involved. At ÂŁ58.
Again fair enough it does need doing.
this is just for my own curiosity really, but if there is no visual bond, how would you test the incoming water to see of there was bonding?
at a guess and please correct me if this is silly, but I would isolate the supply, disconnect the main earth, then do a wander lead test the water to the MET to see if it is bonded.
is that a safe approach to check it?
Interesting to see other people's work, but seems like these guys are at it a bit here.....
He he asked me to look over the report as he thinks he's being ripped off, which I must admit it does reek of.
Firstly for for example it has a C1 for the distribution board for a blank missing. Cost to rectify ÂŁ30!!!
another couple of things which is sounds fair enough like no earth to lights. And there is a metal light in the living room.
But rather than just note this, the guy has stated it needs an earth run to it.
I had a quick look at this problem and opened a switch and it's wired in conduit, presumably with the Cpc being supplied by the metal conduit.
this wasn't noted on the report, nor a further investigation req. to see if that would be viable for the earth.
If it was okay there would be no need for a separate earth to be run and no need for the big cost also involved to do it. Was requesting ÂŁ160 to earth the lights!
I would (if it was me) also have given the option to simply replace the fittings with class 2 fittings, and a label at the board, at a much reduced cost. They didn't give this option or even mention it.
Another point was was the main bonding, the gas is bonded, but no visible bond to water.
But in the report its ticked as okay, then further on saying it needs doing. But it simply states on the follow on work to "investigate main bonding" with no mention of remedial work involved. At ÂŁ58.
Again fair enough it does need doing.
this is just for my own curiosity really, but if there is no visual bond, how would you test the incoming water to see of there was bonding?
at a guess and please correct me if this is silly, but I would isolate the supply, disconnect the main earth, then do a wander lead test the water to the MET to see if it is bonded.
is that a safe approach to check it?
Interesting to see other people's work, but seems like these guys are at it a bit here.....