EICR - square D and schneider MCBs in same board | on ElectriciansForums
Discuss EICR - square D and schneider MCBs in same board in the UK Electrical Forum area at ElectriciansForums.net
North
Guys,
Just a quick bit of advice.
I was conducting a EICR and came across a square D board with all square D MCBs apart from 4 schneider MCBs were they must of been upgrades to the installation.
Are these MCBs compatable with each other? If not am i correct in noting this as a code 3?
thanks maggie
Depends on which generation you have - Merlin / Schneider MCB's are exactly the same as KQ (modern range) Square D, they are made in the same factory by the same machines except the Square D has a 2 prong clamp fitted, if you take that clamp off - you have a Merlin / Schneider albeit stamped with different name.
You can't take the clamp off now with the Square D as they are glued in , this is so you can not insert into the Merlin Gerlin boards , as the breakers for these boards are nearly double the price
you can grind the buggers off though.
Even the square D type come as schnieder now.
But they fill the screw in with glue so you cant unscrew the prongs. Sneaky!![emoji1]
Reply to EICR - square D and schneider MCBs in same board in the UK Electrical Forum area at ElectriciansForums.net
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...