Hi all, iv recently passed my testing and inspection course and have landed a job doing EICRs iv noticed that people I work with are ticking all the boxes in the section for "other methods of protection" I dont believe they should be. Can anyone give me a break down of what each point means exactly and give an example just so I am clear in my mind I'm understanding the tick sheet properly. Thanks .
 
Hi all, iv recently passed my testing and inspection course and have landed a job doing EICRs iv noticed that people I work with are ticking all the boxes in the section for "other methods of protection" I dont believe they should be. Can anyone give me a break down of what each point means exactly and give an example just so I am clear in my mind I'm understanding the tick sheet properly. Thanks .
Google DPN5 tick sheet explained
 
Other methods of protection is not included on the Inspection Schedule for an EICR unless yours differs to the format in BS7671.
 
You are mostly correct. It would be extremely rare for an installation to adopt all these methods of protection:

Double Insulation is cables that are insulated twice. Such as meter tails.

Reinforced must meet the same protection as above but are only insulated once.

Use of Obstacles would be physical barriers to prevent touching of live bus bars for example.

Placing out of reach would be live bus bars put high up so that they are out of reach.

Earth-free local equipotential bonding would be when all exposed conductive parts are connected together but not connected to an earth.

Electrical Separation is when an air-core transformer is used for protection.

It is important to add that the above can only be ticked if ADS does not apply. So if you have SELV downlights then if the lighting circuit is protected by ADS then you don't need to tick 'Electrical Separation' also.
 
You are mostly correct. It would be extremely rare for an installation to adopt all these methods of protection:

Double Insulation is cables that are insulated twice. Such as meter tails.

Reinforced must meet the same protection as above but are only insulated once.

Use of Obstacles would be physical barriers to prevent touching of live bus bars for example.

Placing out of reach would be live bus bars put high up so that they are out of reach.

Earth-free local equipotential bonding would be when all exposed conductive parts are connected together but not connected to an earth.

Electrical Separation is when an air-core transformer is used for protection.

It is important to add that the above can only be ticked if ADS does not apply. So if you have SELV downlights then if the lighting circuit is protected by ADS then you don't need to tick 'Electrical Separation' also.
The tails you describe as double insulated, are not Double insulated, they are an insulateD single cable with a PVC mechanical protective sheath, the same as Twin and CPC.
 
Tails are not double insulated. They have the basic insulation and then sleeving just like twin and Earth and that isn't called double insulated.

The tails you describe as double insulated, are not Double insulated, they are an insulateD single cable with a PVC mechanical protective sheath, the same as Twin and CPC.

Both tails and T&E meet the definition of 'Double Insulated' which is 'Insulation comprising both basic insulation and supplementary insulation'.

Furthermore Regulation 412.2.4.1 further clarifies this.
 
Both tails and T&E meet the definition of 'Double Insulated' which is 'Insulation comprising both basic insulation and supplementary insulation'.

Furthermore Regulation 412.2.4.1 further clarifies this.
Can't see the a square within a square symbol on any tails I have installed Essex, have you? and how does that regulation clarify your statement? I agree it may be called reinforced insulation, or mechanical protection of basic insulation. but NOT double insulation.
 
Last edited:
Can't see the a square within a square symbol on any tails I have installed Essex, have you? and how does that regulation clarify your statement? I agree it may be called reinforced insulation, but NOT double insulation.

Note 2 of that Reg states that cables should not be identified with the double squared symbol.

If you read the Reg it states that a cable installed that is rated no less than the nominal voltage and has basic insulation and a non-metallic sheath (DI tails and T&E) then the cable will meet the requirement of Reg 412.2. 412.2 is electrical equipment that is double insulated (square within a square).
 
I often find this Regulation somewhat tenuous in particular where it refers to the insulation considered as providing at least the requirements for reinforced insulation, this I assume does not include any sheathing or containment. Nevertheless this is what it states but I have never bought it.
 

Reply to EICR tick sheet other methods of protection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
155
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
520
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
465

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
Definitely, although most likely within the accessories. I've often found that once accessories are disconnected the cabling IR is fine. Sometimes...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top