EICR today Mains smoke detectors interlinked | Page 2 | on ElectriciansForums

Discuss EICR today Mains smoke detectors interlinked in the UK Electrical Forum area at ElectriciansForums.net

Joined
Feb 26, 2019
Messages
27
Reaction score
18
Location
Stafford
Good evening all
3 buildings :
1 Gf flat and 1St fl flat year 1915
2nd 6 flats year 1980
3rd cottage year 1900
They are separate buildings probabley 2in between them, 1 landlord owns all,
I ve done EICR on 1st building and 1 flat in 2nd building and found that the mains smoke detectors are interlinked hard wired between buildings no local isolation in buildings and not come across the power source that supplies them.
? What code
? Am I going mad is this allowed
 
This is a very interesting discussion about the interlinking of different types of alarms but I think the OP's query was more to do with having the same circuit running through several properties. I had a similar thread a while ago although it was to do with external lighting in a commercial situation. Most of the advice on here was to fit labels in all of the properties which the circuit was present in stating where to isolate it.
 
This is a very interesting discussion about the interlinking of different types of alarms but I think the OP's query was more to do with having the same circuit running through several properties. I had a similar thread a while ago although it was to do with external lighting in a commercial situation. Most of the advice on here was to fit labels in all of the properties which the circuit was present in stating where to isolate it.
As I said in my post number 7.
Perhaps the OP could chime in to help with some clarification...
 
If the smoke alarms are powered from a different supply to the building they are in, then there should at least be warning notices that there is more than one source of supply.
Though I don't see the purpose or reasoning behind having smoke alarms interlinked between separate buildings.
Further investigation would be beneficial.
Thank you, this is the case. Person in one flat told me they ignore it and put it down to false alarm , not knowing that all buildings are interlinked just find it mad, if 24v fire alarm system would not question it but mains really.
Thanks for all the replies stevie g
 
Good evening all
3 buildings :
1 Gf flat and 1St fl flat year 1915
2nd 6 flats year 1980
3rd cottage year 1900
They are separate buildings probabley 2in between them, 1 landlord owns all,
I ve done EICR on 1st building and 1 flat in 2nd building and found that the mains smoke detectors are interlinked hard wired between buildings no local isolation in buildings and not come across the power source that supplies them.
? What code
? Am I going mad is this allowed


I'm still trying to get my head around the statement that there is only 2in between the buildings?
 
I'm still trying to get my head around the statement that there is only 2in between the buildings?
Op, do you mean there are Aico hard wired and interlinked smoke alarms in a house that is now two flats, and then a few doors down the street with neighbours in between, there is another house converted into flats with smoke alarms on the same circuit? And you do not know what house even powers this circuit?
 
Op, do you mean there are Aico hard wired and interlinked smoke alarms in a house that is now two flats, and then a few doors down the street with neighbours in between, there is another house converted into flats with smoke alarms on the same circuit? And you do not know what house even powers this circuit?
3 buildings next to each other nobody in between and yes to rest
 
If it’s tested out fine. It’s safe for continued use. No code.
possible an observation only, but bs7671 doesn’t care if there interlinked or not. It doesn’t care if the smokes don’t work. It’s the hard wiring and safety your ascertaining.
 
If it’s tested out fine. It’s safe for continued use. No code.
possible an observation only, but bs7671 doesn’t care if there interlinked or not. It doesn’t care if the smokes don’t work. It’s the hard wiring and safety your ascertaining.
But does bs7671 have anything to say about a circuit running through several properties (regardless of what equipment it is supplying)? I think that is the original question rather than whether or not the smokes were interlinked and working.
 
Seems strange that except for the requirement of notice's of alternative supplies and where to isolate them, I can't find anything that would mean it was against regulations, your challenge for the rest of the week-end is to prove or diss-prove this, off you go, my OH has just opened a bottle of red.?
 
thanks all for response, have already put on the ecir F/I and alternate supply to cover myself on the 4 flats already done, update further if I do come across the supply at moment loop impedance taken from each smokeand noted on each cert. thanks again
 

Reply to EICR today Mains smoke detectors interlinked in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top