EICR - Unsatisfactory | Page 2 | on ElectriciansForums

Discuss EICR - Unsatisfactory in the UK Electrical Forum area at ElectriciansForums.net

Joined
Oct 14, 2020
Messages
3
Reaction score
0
Location
Sunderland
Hi,

I am about to get an EICR done on a residential property. If a cooker isolation switch is less than 300mm from the hob will this produce an unsatisfactory.

Thanks.
 
The building regulations require you to be 100mm from the hob, not 300mm plus it’s a building regulation for new builds and similar, nothing to do with bs7671 which deals with the suitability of the external influences etc
For the picture and if no evidence of thermal damage it’s only a C3 at the most, never a C2.
 
NAPIT - brought to you by the letter C and the number 2.
The way things are going, Napit registered electricians will find themselves not getting calls for EICRs if the word gets out amongst landlords that they are coding more harshly.

Codebreakers may be a good idea, but there needs to be consistency between organisations and guidance, not competition so you can pick and choose which one you want to follow.
 
Been told switch is in a cooker zone and Napit code it as C2.
Have you had the EICR yet, or was this from another source?

Napit don't code anything - though they produce a book "Codebreakers" that gives example codes for various situations. The inspector makes a judgement on the day based on a variety of factors, so it's not just a simple 'tick box' exercise, or rather shouldn't be. Any code, but in particular C2s or C1s should be backed up with a regulation number that has been breached.

Unfortunately, The Codebreakers book seems to differ in some areas from other guidance available from people like Electrical Safety First.

Their Best Practise Guide states that a C2 is appropriate for

"Fixed equipment does not have a means of switching off for mechanical maintenance, where such maintenance involves a risk of burns, or injury from mechanical movement",

But in this case there is a means of switching off. Does the same switch also isolate the oven?

The socket is potentially an issue but personally the only way I could see it being a C2 is if that was the only socket in the kitchen so was likely to be used for trailing leads. I assume that's not the case?
 
since when did nappies write the regs.?
If they wanted to, the first should probably take out the statement by the Health and Safety Executive on page 13 that makes it very clear that existing installations installed to a previous version are not considered unsafe just because they do not meet current regs.
 
Last edited:

Reply to EICR - Unsatisfactory in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
519
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
754
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

And I'll hazard a guess that when the report does finally turn up, it'll be "a bit vague" as to the actual faults. There have been numerous...
Replies
6
Views
537
Here the BPG#4 is useful, it is not a statutory document at all, but it provides good guidance as to what can reasonably considered as C1/C2/C3...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top