Eicr ..what code would you give | Page 2 | on ElectriciansForums
Discuss Eicr ..what code would you give in the UK Electrical Forum area at ElectriciansForums.net
neath
Doing an eicr ... shed.circuit ...6mm swa feeding shed cu.. 3 sockets(32a) mcb lights( 6 a ) fed direct from main switch output ...what code would you give
C2, but the amount of noise I would make about it would depend on the loop impedance and the size of the bullet 'protecting' it. One coud anticipate some nasty scenarios if the cable gets damaged near the shed end if the impedance is too high.
Reply to Eicr ..what code would you give in the UK Electrical Forum area at ElectriciansForums.net
The cable is way undersized. If the voltage drop is detrimental to the installation I would make a mention of it as volt drop generally is not...
Haha yes, it is. Must be a northern expression. Have a Google 😂