Agreed. I was just taught to use the table over adiabatic on new work but perfectly acceptable if the calcs stack up.
Why? So that you can throw money down the drain oversizeing cpcs?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss eicr in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Agreed. I was just taught to use the table over adiabatic on new work but perfectly acceptable if the calcs stack up.
How can you apply the adiabatic equation to size an earthing conductor on a tn-c-s when it is supposed to be sized in accordance with the sizing of the main protective bonding. The adiabatic equation is used on tn-s & t.t installations and normally is used to confirm adequacy of existing earthing conductors on said existing installations. For new work the relevant tables in BS7671 for sizing of protective conductors in tn-s / t.t installations should be used.
Just had it pulled on me on numerous occasions over the adiabatic but still your point is very valid.
So what? People have attempted to pull me up on all sorts of things yet come unstuck when they can't back it up with proof.
Had argument with my boss today regarding pulling in a 10mm earth from main intake to flat ccu he goes if the main bond to gas and water is 10mm and goes to main intake met why don't I just get the 10mm earth off there in to the ccu met to make it 16mm as it already has 6mm. I told him it's like bonding from ccu met to gas or water. needs to go direct to intake met he told me just f do it so I told him no and I will refuse to sign it as satisfactory
The earthing conductor size is calculated by the adiabatic equation. This size is then divided by 2 to get the bonding size.
The bonding in a PME supply is related to the supply neutral, but not all TNCS is PME.
I am not your son! I find it insulting and derogatory that you would call me such. Please don't call me that, or any other derogatory name you can think of.
Why does it have to go directly to the intake?
I always belived main earth had to go direct to intake seen as the main gas and water has been bonded in 10mm from main in take met I wasn't sure if I could just get the 10mm required from the gas or water bond and take that to the ccu met to make it 16mm I like to be sure before I do anything
I always belived main earth had to go direct to intake seen as the main gas and water has been bonded in 10mm from main in take met I wasn't sure if I could just get the 10mm required from the gas or water bond and take that to the ccu met to make it 16mm I like to be sure before I do anything
Please elaborate on the difference between tn-c-s and a PME to clarify your point on this matter.
Please elaborate on the difference between tn-c-s and a PME to clarify your point on this matter.