Exactly right,the actual incoming neutral size is 240 mm,which I think gives a Earth bonding conductor of 50 mm.
Interesting to know the C3 code given
Hi Cliffed, to clarify - the 4 core 35mm SWA is used to extend the 3 phase service from the TNCS PME DNO cutout. There are no connections to the cutout except via this SWA, so the armour is providing CPC for the SWA and earthing conductor function for the site?
4 core 35mm SWA has steel of 84mm and resistivity ratio given as 8.5 on p60 of GN8 meaning equivalent to 9.88mm of copper. Which means its undersized for current regs, which I think will be 10 or 16 from Table 54.8 (depends on incoming DNO neutral size).
I'm not familiar enough to know if it was sized ok for an earlier edition? In which case it could be a C3 improvement?
I thought the ratio was 8, not at home to check.
Reply to EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...