Doing an eicr within a mechanical work shop coding on this guys what’s your views? Copper showing of tails c1 single insulated tails not mechanically protected ?
 
TL;DR
Eicr
First impression, without thinking too long about it...
C2 for the single insulated tails, seems to apply to other henley blocks too
Another C1 if it's possible to actually touch that copper, otherwise C2

(IMHO quicker to fix the exposed copper tail than code it if client is willing.)
 
First impression, without thinking too long about it...
C2 for the single insulated tails, seems to apply to other henley blocks too
Another C1 if it's possible to actually touch that copper, otherwise C2

(IMHO quicker to fix the exposed copper tail than code it if client is willing.)
Thanks mate
As above would take 5 minutes to re-terminate , if the job allows for
I always try and get permission to fix small quick things. Rarely is this refused!
My pet hate is seeing "Missing 2 Colours sticker" or "Missing RCD Test Label" on a report, I want to scream "just slap one on!"
Get this a lot mate with stickers etc, due to this being in full production it’s a bit harder to just shut stuff down so arranged with clients for a sat morning shut down quick fix
 
First impression, without thinking too long about it...
C2 for the single insulated tails, seems to apply to other henley blocks too
Another C1 if it's possible to actually touch that copper, otherwise C2

(IMHO quicker to fix the exposed copper tail than code it if client is willing.)
Bit concerning the poor IP ratings on the Henley blocks.
 
Looking at the henley block in the foreground of the picture is the bottom corner damaged or has it become brittle due to the material aging
 
Looking at the henley block in the foreground of the picture is the bottom corner damaged or has it become brittle due to the material aging
Yep good shout. This is fast becoming "replace Henley blocks"

Heads up for the OP, don't mount new ones on the wall neatly touching each other, you won't get the covers on afterwards!
Never done that, honest ?
 

Reply to Eicr in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
707
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

That is what i am going to do. Thanks mate!
Replies
11
Views
786
I would C2 this, cable is not suitable for the environment its installed in, we would C2 a socket for equipment likely to be used outside , cable...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top