I'm on a TT system through supplying cables that run underground, but then along the front of the house just above the front door.
I have an ELCB which trips ocassionaly, and when it does it is sometimes difficult to get it to re engage. Because of this I have been meaning to replace this or the CU which is an older wylex with the fuses replaced by mini MCB's. From memory the earth measured 17 ohms at the CU.
Whilst on holiday the ELCB tripped, and was only noticed when my neighbour popped in to move the post, and he realised the lights didn't work. He couldn't get the ELCB to turn back on as there is quite a knack to it. In an attempt to save my freezer contents I asked a friend to have a quick look, and he tried to fit a 30ma RCD in place of the ELCB. This tripped out immediately, so as a temporary measure the ELCB was refitted which he managed to get it to turn back on.
When I got back I got a 100ma RCD thinking that would work ok rather than the more sensitive 30ma. However this tripped again immediately the power was turned back on, so I have a problem somewhere which I need to sort.
I've now decided I would like to get the CU replaced, but I am reluctant to do this until I have found the fault (s) causing the trips, or at least narrowed it down.
Yesterday I decided I would see if I could narrow down the problem circuits. The difficulty with this is that it has a single ring main for both floors, another for the lights, a 3rd for the hob and immersion heater and a 4th for the outside light, so even narrowed down it would still be quite a broad area.
What I discovered was that on the lights, if I turned on the lounge lights the RCD (100ma) would trip. This is a two way switched circuit, with one switch being a dimmer. The bathroom lights would also trip the RCD. These are controlled by a ceiling mounted PIR. All other lights were ok.
On the ring main, as soon as the MCB was switched on it tripped the RCD. I was running out of time so wasn't able to unplug everything, and so decided to leave it for another day.
What is puzzling me is that I have numerous faults which I know is a possibility, but I was speculating I may have one fault that is causing this behaviour.
My friend is coming back to meg the cables which he couldn't do whilst I was away as he didn't know where every socket was in the kitchen so didn't want to risk damaging any appliances.
Apologies for the long first post, but suggested ideas for causes would be appreciated. Could the TT system be a factor? Central Networks charge £150 to change to PME, although I haven't checked if I could actually get this at my property.
Justin
I have an ELCB which trips ocassionaly, and when it does it is sometimes difficult to get it to re engage. Because of this I have been meaning to replace this or the CU which is an older wylex with the fuses replaced by mini MCB's. From memory the earth measured 17 ohms at the CU.
Whilst on holiday the ELCB tripped, and was only noticed when my neighbour popped in to move the post, and he realised the lights didn't work. He couldn't get the ELCB to turn back on as there is quite a knack to it. In an attempt to save my freezer contents I asked a friend to have a quick look, and he tried to fit a 30ma RCD in place of the ELCB. This tripped out immediately, so as a temporary measure the ELCB was refitted which he managed to get it to turn back on.
When I got back I got a 100ma RCD thinking that would work ok rather than the more sensitive 30ma. However this tripped again immediately the power was turned back on, so I have a problem somewhere which I need to sort.
I've now decided I would like to get the CU replaced, but I am reluctant to do this until I have found the fault (s) causing the trips, or at least narrowed it down.
Yesterday I decided I would see if I could narrow down the problem circuits. The difficulty with this is that it has a single ring main for both floors, another for the lights, a 3rd for the hob and immersion heater and a 4th for the outside light, so even narrowed down it would still be quite a broad area.
What I discovered was that on the lights, if I turned on the lounge lights the RCD (100ma) would trip. This is a two way switched circuit, with one switch being a dimmer. The bathroom lights would also trip the RCD. These are controlled by a ceiling mounted PIR. All other lights were ok.
On the ring main, as soon as the MCB was switched on it tripped the RCD. I was running out of time so wasn't able to unplug everything, and so decided to leave it for another day.
What is puzzling me is that I have numerous faults which I know is a possibility, but I was speculating I may have one fault that is causing this behaviour.
My friend is coming back to meg the cables which he couldn't do whilst I was away as he didn't know where every socket was in the kitchen so didn't want to risk damaging any appliances.
Apologies for the long first post, but suggested ideas for causes would be appreciated. Could the TT system be a factor? Central Networks charge £150 to change to PME, although I haven't checked if I could actually get this at my property.
Justin