Hello,
I have following scenario, 20A circuit breaker in the CU. 3 x 2.5 SWA cable feed to a garden shed CU. In the shed CU I have 0.69 ohm on the income cable. On the shed are two 16A radial circuits of socket outlet. When I do Ze on the sockets , I get 2.9 ohms.
The radial circuits have 2.5mm2 flat cable no longer than 5m from the shed CU.
Any idea why is the reading so high please?
 
it is the perennial power to a shed post. there should be a separate forum on this site for anything to do with running power to a shed or garage. maybe we could make a lovely step by step diagram and guide on how to do it, how to test etc... as a week doesnt go by without the same questions cropping up. I do recall the IET and NAPIT making a similar guide a few years back - wiring matters? it was simple enough to follow, only thing is the diy'ers started getting to work causing chaos.

Theres an idea. electriciansforum pdf files or little guidance notes. all nicely branded and sold to folks out there... could be lucrative for the site!!
 
In the grand tradition of shed-threads......Somebodies got to suggest TT-ing it. I volunteer.

TT the b****r.

[ElectriciansForums.net] elec. power to a garden shed
 
I actually wired a shed this very day. 4mm all the way SWA then T&E and Zs of 0.63 at the furthest socket. :)
your MBE is in the post. ( send cheque to Campaign for Attention of Shire Horses. if that's a bit too long, just use the abbreviation C.A.S.H. ).
 
It wasn't meant to be anything special Tel, just coincidence that I wired a shed today, so thought I'd add a little bit of boring detail. Must say the surface clipping was lovely though. :D
 

Reply to elec. power to a garden shed in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
It’s all a bit confused as he originally says I read that as with supply removed he was picking up 230v. My concern is/was that as the house...
Replies
13
Views
3K
  • Question
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...
Replies
7
Views
1K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
646
  • Question
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
    • Like
    • Winner
Replies
0
Views
587
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks