Nicktric
Hi again,
I have done a CU change for my assessment and just want to run a few more things past you if I may before the big day? I have a 2.5mm socket radial supplying two points for my minor, I would have put this on a 20A breaker but the board (my major) only came with a 16A should I upgrade to 20A or not necessary and why don't they supply 20A MCBs with new boards when the regs state 20A for radials?
I don't want to get caught out on this as I know it is a common question:
Are these correct?
General purpose RCDs to BS61008 should trip under 300ms
GP RCD's to BS4293 should trip under 200ms
Socket RCD to BS7288 should trip under 200ms
An RCD not exceeding 30ma should trip at 40ms at 5 times operating current
But the max disconnection time on a TN is 400ms so why should a GP RCD to BS61008 trip under 300 and not 400ms?
When he asks me what time should the rcd trip on a TNCS is it 300 or 400ms as EGtoBR states 300ms and 7671 states 400ms, I know I'm missing something..
Cheers!
I have done a CU change for my assessment and just want to run a few more things past you if I may before the big day? I have a 2.5mm socket radial supplying two points for my minor, I would have put this on a 20A breaker but the board (my major) only came with a 16A should I upgrade to 20A or not necessary and why don't they supply 20A MCBs with new boards when the regs state 20A for radials?
I don't want to get caught out on this as I know it is a common question:
Are these correct?
General purpose RCDs to BS61008 should trip under 300ms
GP RCD's to BS4293 should trip under 200ms
Socket RCD to BS7288 should trip under 200ms
An RCD not exceeding 30ma should trip at 40ms at 5 times operating current
But the max disconnection time on a TN is 400ms so why should a GP RCD to BS61008 trip under 300 and not 400ms?
When he asks me what time should the rcd trip on a TNCS is it 300 or 400ms as EGtoBR states 300ms and 7671 states 400ms, I know I'm missing something..
Cheers!