Surely a safety inspection of an unvented hot water system should include checking the functions of any safety thermo-stat and over pressure relief valve.
a failure of these devices could lead to an explosion.
Surely a safety inspection of an unvented hot water system should include checking the functions of any safety thermo-stat and over pressure relief valve.
a failure of these devices could lead to an explosion.
Agreed, but the problem with testing over-pressure relief valves is that they very frequently never seal properly again... resulting in a permanent pressure leak hence forward... until they finally get replaced years later.