Electric Gate Wiring Question? | on ElectriciansForums

Discuss Electric Gate Wiring Question? in the UK Electrical Forum area at ElectriciansForums.net

Joined
Dec 23, 2018
Messages
7
Reaction score
0
Location
Ireland
I have a 455D FAAC gate and associated control panel. I need the gate to stay open on command and not close after a pre-determined time but to do this, according to page 5 on the manual (link here), I must do the following:

"OPEN/HOLD OPEN DEVICE: To open and hold open the gate, simply maintain a contact across terminals 9 and 14. (“A” Mode only) "

My question, what does "maintain a contact across terminals 9 and 14" mean. Do I need a wire to run a permanent wire between the two terminals? At the moment there isn't one connecting the two. (see image)

Thanks!

[ElectriciansForums.net] Electric Gate Wiring Question?
 
You need to put a latching switch across 9 and 14 . 14 is the open comand, turn the switch on gate opens and stays open turn switch off and gate will close after the hold time, only works in mode A though .
 
song.

"Oh Danny Boy, the gates, the gates are calling,
Down by the Glen and valleys down below,
We open up as when you are calling,
but shut before you get the carriage through"
 
Ahhh ok. So if I run a cable from 9 to 14 I'm sorted? Thanks

A cable, is not a switch. If someone says install a latching switch, it's not very polite to ask them to confirm that you just need to common the two contacts in question.

I can't help but think your best 'sorted' by replacing the cover, and politely excusing yourself from this job.

If you don't know what a latching switch is, it's probably best not to attempt installing one. I'm not entirely certain what a heart splint is, but if any of my older relatives ever need one fitting, I'll stick to my own advice and let someone who does know do the job ;)
 

Reply to Electric Gate Wiring Question? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...
Replies
4
Views
2K
  • Question
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top