Browsing to buy a new electric oven. I came across a Hotpoint with a rating of 10.7 kWh. I calculated that would need a 16mm cable! Surely not? I multiplied by 1.25 as when it's on its a continuous draw. Thoughts?
 
Diversity is your friend here.

From memory as not got my regs book to hand…

The first 10 amps + 30% of remaining load + 5 amps if your cooker isolator switch has got an integrated socket on it.

If my maths is right, it should draw just shy of 26 amps with diversity applied.

So depending on the length of run and installation reference method, it should be good on a 6mm cable and a 32amp MCB/RCBO
 
what he said. ^^^^^^^^. rare to find that you need to go up to 10mm cable. the 6.0mm cable is protected against overload by the 32A MCB. both cable and MCB will withstand 40% overrrating for up to 1 hour when the load exceeds 32Aif all elements are warming simultaneously ( woow, spelloing at 5.00a.m.after beer. I must getoutmore).
 
Browsing to buy a new electric oven. I came across a Hotpoint with a rating of 10.7 kWh
Just an oven, not a complete cooker, correct?
kWh (kilowatt hours) is a measure of energy usage. The electrical load rating (from which the current is calculated) is measured in kW (kilowatts). I don't think the oven uses 10.7kW unless it is a huge commercial thing, domestic ovens are typically no more than 4kW and many are less.

What is the actual rating in kW?
 
Last edited:

Reply to Electric oven cable size in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
To be honest James I use an app- Electrical Calculations. It auto calculates the cable size once you enter the specifics/parameters. Voltage...
Replies
5
Views
1K
  • Question
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...
Replies
2
Views
188

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top