Hi, my neighbour has had to change his electric shower (6kw) pull switch (32A) 3 times in 4yrs. Apart from it possibly being poor quality switches he,s replacing, I was wondering if there is any reason not to leave the pull switch isolator in the "on" position. Thanks
 
Still wondering what Charlie,s points were ?
Still wondering what Charlie,s points were ?
Whilst I don't want to steal Charlie's thunder, but the point he is making is a valid one, the higher the KW of the shower the bigger the spark should there be a faulty connection, basivc Ohms Law I = P/V 6000/230=26 Amps whereas 9000/230=39Amps
The other points I'll leave to Charlie but I'm sure you get the gist of what Charlie
said cuz I 'm nice like that, shut up TEL.
 
Last edited by a moderator:
Whilst I don't want to steal Charlie's thunder, but the point he is making is a valid one, the higher the KW of the shower the bigger the spark should there be a faulty connection, basivc Ohms Law I = P/V 6000/230=26 Amps whereas 9000/230=39Amps
The other points I'll leave to Charlie but I'm sure you get the gist of what Charlie
said cuz I 'm nice like that, shut up TEL.
Yes, but if the switch is rated to take the load, it should be fine ?
 
If I went to a job where a shower was up to a 4th isolator in as many years and I knew my previous connections were good then I would also inspect the shower and iland test it for any problems.. especially if the shower is only 25 amps
It was "only" 3 isolators, and I don,t know what could cause an isolator to burn out due to something being wrong in the shower unit ? How could that affect the switch contacts ?
 
It was not switched off under flc
It was "only" 3 isolators, and I don,t know what could cause an isolator to burn out due to something being wrong in the shower unit ? How could that affect the switch contacts ?
Not doubting your sincerity Clem, but how do you know that? if there is a duff connection then contact burnout will occur. Bite the bullet and fit a decent wall isolator
 
It was "only" 3 isolators, and I don,t know what could cause an isolator to burn out due to something being wrong in the shower unit ? How could that affect the switch contacts ?

You said you had replaced it 3 times in 4 years??
Inside shower; faulty components, low ir, reverse polarity could all affect the isolator
 

Reply to Electric shower pull switch isolator in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Better off with the click prw213 as it has twin screw termination.
Replies
9
Views
984
I thought that too, but I didn’t want to upset the old fella by telling him 😛
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top