You need to take the size of your shower and divide it by the voltage then check the rating if the cable..

What voltage would you use, and how would you go about cross referencing the cable size, what about termal efects, downrating cables and allowing for BS3036 fuses, volt drop?????
 
rule of thumb is 9.5kW if cable is clipped direct with a 40A MCB. obviously if cable needs derating due to insulation, the cut-off kW for 6mm would be lower.
 
I would personally upgrade to 10mm anyway, as most showers these days demand quite a high current.

but I think the figure you're looking for is 8.5kW...

also depends how the cable is run, what length etc
 
What voltage would you use, and how would you go about cross referencing the cable size, what about termal efects, downrating cables and allowing for BS3036 fuses, volt drop?????

Absolute worst case scenario, ok...

Day to day general thinking, its not exactly relevant. When installing you know when the above becomes relevant because it would be a nightmare of a job.

The OP didn't provide such detail in his question, therefore I provided the basics in my reply. Which you will find is correct.

Edit: Sorry I missed out some of your questions.

Measure voltage at the source, or if a quote go by 230v.

Checking current carrying capacity is checked with whatever table it is in the regs compared with the reference methods and fuse types etc.

Is this sufficient?
 
Last edited by a moderator:
Even 10mm can be underated what with all the massive amounts of insulation i have seen going into lofts covering just about everything. method 101 36 amps will just about support 8.5 kw.I would be interested to know if all these insulation companies worry about cable ratings? There are so many things that have to factored in when selecting a cable these days.
 

Reply to electric shower in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
295
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
277
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

Hi, i am wondering if anyone has any experience with a 7.5-8kw shower that has a pump or some sort of boost internally fitted? Working at a hotel...
Replies
0
Views
203

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...
  • TT advise
    OK My take on the precautions to implement when omitting an up front RCD on a TT system. Tails...
  • SIL vs ATEX
    Good morning all, I have a question for those who are CompEx and SIL aware - I have various Ex...
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top