To clarify, although there is a label mentioning RCD testing proecdure on the board, there are no RCDs. The breaker that is tripping is an MCB, equivalent to a fuse. For it to trip there must be either an overload (e.g. too many appliances) or a short-circuit (e.g. wires touching together). If everything is unplugged and there is no undiscovered 'herbal laboratory' in your loft that the circuit is powering, then there is most likely a damaged cable that is intermittently shorting. Unlike an RCD trip caused by modest leakage to earth, the heavy current required to trip an MCB makes the fault a potential fire risk due to arcing and overheating. You should not keep resetting the MCB; the fault must be found and rectified even if the MCB stops tripping as it will otherwise remain a risk.
Anyone who looks for the cause of an MCB trip using a socket tester isn't an electrician.