Hi all, wondering if anyone can help me with a recent issue I've had with electric UFH in a small flat. Found that when the UFH starts, the RCD trips immediately - this started last Saturday while I was away. Prior to this, I had heard some buzzing coming from near the UFH unit controller in my kitchen, but didn't realise there was an issue.

Here are some details of the system
  • Controller: TH-132 (15A RES Max.)
  • Mat area (total) ~ 5m2 (covers a small kitchen and hallway)
  • Installation Date ~2005 (it was installed before I moved in, so I don't have any manufacturers details / specs)
I did some checking yesterday and noticed that the UFH controller is fed from a wall socket in the kitchen. When I opened the socket, I noticed the earth had come free of the terminal, and there was some evidence of arcing damage on the live wire at the terminal also. I pared back the line and earth, and refitted them, thinking this might solve the problem (and might have explained the buzzing I'd heard). When I reconnected the UFH, the problem was still there, and the RCD tripped immediately.

So, pulled out the multi-meter and ran a few tests. Results as follows:
  • Tested resistance across mat (LOAD L/N) = ~28 ohms
  • L-E > 1 Mega Ohm
  • N-E = 29 ohms
I am writing this post from memory of the readings I took yesterday so I may be slightly off. As I don't know the spec of the heating mat, I have to assume the resistance reading I got on the mat seems reasonable, as it would equate to ~8.5A current (which I assumed was about right given what I've seen for a system this size (here's the resistance table I was comparing from another manufacturer).

Insulation test on Line to earth seems okay, but Neutral to earth is not? Am I correct in thinking I should be getting the same reading across both of this. When I carried out the test, the RCD was off, but Main switch was on.

Does anyone have any idea what the problem might be, or what further tests I should carry out to diagnose the issue? Was hoping this was a problem with the main wiring or controller, as I can't afford to take up teh floor right now, and it's not going to be a fun Christmas in Scotland with no heating :(.

Any help is much appreciated
 
as hhd said, dis. the mat leads completely from the contoller and IR test them. L-E and N-E.... L-N should read on continuity, anything from 20 ohms upwards depending on the wattage rating. if those readings are good, then look back towards the socket.
 

Reply to Electric Underfloor Heating - Tripping RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
It's the policy on this forum not to give step by step advice. If you have an understanding of wiring requirements you will not have any...
Replies
1
Views
1K
Ok I’ll try this when I’m down
Replies
4
Views
355

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top