S
Stugadget
I will shortly be installing POD Point Electric Vehicle Charging units and I am very confused by the earthing requirements if the property has a TN-C-S Supply.
I have read the installation manual of the POD Point, Amendment 2:2013 of BS 7671:2008 and the IET Code of Practice for Electric Vehicle Charging Equipment Installations.
My initial thoughts were that if the car was to be charged outside of the house then I could not connect to the PME earth terminal and I would have to make the circuit a TT by the installation of an earth rod.
I found this article on the NET Electric Vehicle Charging | Professional Electrician & Installer and the last paragraph states "Based on the HSL report, the decision was taken to permit the use of PME supplies to charge electric vehicles – subject to the requirements of Regulation 722.411.4. "
Regulation 722.411.4 is in Amendment 2:2013 of BS 7671:2008 which is reprinted in the second part of the article Electric Vehicle Charging: Part Two | Professional Electrician & Installer the author has added this paragraph.
"An exemption is made for dwellings. None of the following requirements need be applied for the charging point at a dwelling if it is not reasonably practicable to do so. This means that the requirements of this regulation may or may not be applied to a dwelling. "
What gives the author the authority to add that paragraph as its definitely not in Amendment 2 :2013 ?
So what is your opinion can I connect the earth of the Charging Point to the main earth connection in a house with a PME supply ?
I have read the installation manual of the POD Point, Amendment 2:2013 of BS 7671:2008 and the IET Code of Practice for Electric Vehicle Charging Equipment Installations.
My initial thoughts were that if the car was to be charged outside of the house then I could not connect to the PME earth terminal and I would have to make the circuit a TT by the installation of an earth rod.
I found this article on the NET Electric Vehicle Charging | Professional Electrician & Installer and the last paragraph states "Based on the HSL report, the decision was taken to permit the use of PME supplies to charge electric vehicles – subject to the requirements of Regulation 722.411.4. "
Regulation 722.411.4 is in Amendment 2:2013 of BS 7671:2008 which is reprinted in the second part of the article Electric Vehicle Charging: Part Two | Professional Electrician & Installer the author has added this paragraph.
"An exemption is made for dwellings. None of the following requirements need be applied for the charging point at a dwelling if it is not reasonably practicable to do so. This means that the requirements of this regulation may or may not be applied to a dwelling. "
What gives the author the authority to add that paragraph as its definitely not in Amendment 2 :2013 ?
So what is your opinion can I connect the earth of the Charging Point to the main earth connection in a house with a PME supply ?