An electric cooking appliance is to be installed in commercial premises. The circuit is wired using a 12m length of 6.0mm2 PVC sheathed cable clipped direct to a surface, and containing 2.5mm2 CPC. A 45A BS 1361 cartridge fuse protects the circuit and the value of Ze for the installation is given as 0.40 ohms. Assuming that there are no correction factors for grouping or ambient temperature, determine whether the circuit complies with BS 7671 for shock protection? The nominal voltage may be taken as 230 volts and the design current is 45A.
Ib: 45A
In: 45A
It: 45A
Iz: 47A. No correction factors.
VD= 7.3 x 45 x 12/1000 = 3.94
6.0mm2 is acceptable.
Max Zs= 1.04
0.40 + (10.49) x 1.02 x 12/1000 = 0.13
Zs= 0.40 + 0.13 = 0.53
Zs= 0.53
Zs is not above the maximum permitted value of 1.04 ohms and therefore is acceptable.
Have I worked this out correctly? Thanks again for all of you that help me out!