An electric cooking appliance is to be installed in commercial premises. The circuit is wired using a 12m length of 6.0mm2 PVC sheathed cable clipped direct to a surface, and containing 2.5mm2 CPC. A 45A BS 1361 cartridge fuse protects the circuit and the value of Ze for the installation is given as 0.40 ohms. Assuming that there are no correction factors for grouping or ambient temperature, determine whether the circuit complies with BS 7671 for shock protection? The nominal voltage may be taken as 230 volts and the design current is 45A.

Ib: 45A
In: 45A
It: 45A
Iz: 47A. No correction factors.

VD= 7.3 x 45 x 12/1000 = 3.94
6.0mm2 is acceptable.

Max Zs= 1.04

0.40 + (10.49) x 1.02 x 12/1000 = 0.13
Zs= 0.40 + 0.13 = 0.53
Zs= 0.53
Zs is not above the maximum permitted value of 1.04 ohms and therefore is acceptable.

Have I worked this out correctly? Thanks again for all of you that help me out!
 
Looks good, although personally I would up it to a 10mm² if this was a real circuit as the design current and the capacity of the cable are way too close for comfort in my personal and humble opinion. I like to see a good gap of about 10% between the two at least.
 
The latest edition of BS7671 seems to be lacking information for BS 1361 fuses however these are basically the same BS88-3 and the figure for a 45A BS88-3 on a 5 second disconnect is 1.04Ω, 0.57Ω is the nearest quoted to your 0.52Ω and that is a for an 80A BS88-3.

I don't have a regs book with me at the moment, just a table with all the data sets in on my tablet, so if you can find a table for the BS1361 that I missed I will stand corrected.
 
Dave, good call chap, double checked my tables and there I have Table B5 for BS1361 fuses. (really should have looked harder before) and you are correct, the maximum Zs for a 45A is indeed 0.52Ω, significantly different from a BS88-3. In my defense I have not dealt with a BS1361 for a good few years and not had a reason to look one up since college more than 25 years ago!
 
shock protection verification is asking you to prove that the cpc is of sufficiant size to clear the fault current.
you do this with the adiabatic equation.
the question has given you all the values needed to complete the sums.
;-)
 
The latest edition of BS7671 seems to be lacking information for BS 1361 fuses however these are basically the same BS88-3 and the figure for a 45A BS88-3 on a 5 second disconnect is 1.04Ω, 0.57Ω is the nearest quoted to your 0.52Ω and that is a for an 80A BS88-3.

I don't have a regs book with me at the moment, just a table with all the data sets in on my tablet, so if you can find a table for the BS1361 that I missed I will stand corrected.
thats because BS1361s are a redundant number....
you are correct for using BS88-3
 

Reply to Electrical course question help in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top