Who else gets these, unexplainable faults that correct themselves?

Had one today in the site canteen, one of the fryers wasnt working so i checked the supply, 230v at the supply and load end of the isolator, checked at the outlet plate, 36v L - N, Disconnected the circuit and done IR test and came back clear, Didnt have much time on the job so put everything back together, switched it on and it was working fine, iv got no explanation as to what the fault was.
 
had this problem on fryers before. Check your neutrals if your only getting 36v Phase - N whats the readings P-E? if its 230v you may have dropped a neutral

check the voltages inside the unit. I know its greasy but it does help
 
sounds like a poor neutral connection I would suggest you check the teminations. If it goes completly then the metal casing may go live. i had the same problem many years with a servery counter in Bosnia
that folk were gettting shocks from. 63V on metal casing and no neutral
 
sounds like a poor neutral connection I would suggest you check the teminations. If it goes completly then the metal casing may go live. i had the same problem many years with a servery counter in Bosnia
that folk were gettting shocks from. 63V on metal casing and no neutral

will have another look tomorrow, its vital for the breakfast :)
 
Used to be regular on some of the plants I worked on.
½ mile trek to the faulty bit of kit, get there and start testing. Can’t find anything wrong, shout the control rum to t give it a try, off it goes. Hadn’t done a thing!
 
Get in early! If you are nice an early and you get special treatment from the chefs? I am guessing from the Light Infantry badge its a MOD site

No that was a long time ago, its just your bog standard building site, i did get a free lunch for FIXING it today

- - - Updated - - -

Used to be regular on some of the plants I worked on.
½ mile trek to the faulty bit of kit, get there and start testing. Can’t find anything wrong, shout the control rum to t give it a try, off it goes. Hadn’t done a thing!

Its a pain but looks like you know what your doing haha
 

Reply to Electrical Gremlins in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
1K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
980

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top