Deleted member 138473

Hi

When filling out EIC forms under a few sections (design, construction) it asks to fill in the empty line with dates for an amendment of BS7671:2018.

Will this date be 2020 now as the first amendment has been released.

I was told to N/A this part by a tutor.

Thanks.
 
A question on disconnection times for new distribution circuits.

I have been pulled up by the NIC for not proving to meeting disconnection times on two different certificates, highlighted below.

The single phase circuit is from a TN system and supplies a converted bus using a TT system. The cable has had the SWA and CPC isolated in an insulated box, using only the local earth stakes and bonding.

The 3 phase circuit is from a TN DB to a new DB in the same building.

From the NIC - "provide evidence showing that the two Sub mains circuits installed at the two sites attended meet disconnection time stated in regulation 411.3.2.3 and 411.3.2.4"

The below apparently does not satisfy the requirement, and I'm just not seeing the issue.

Any help greatly appreciated.

Mick

[ElectriciansForums.net] ELECTRICAL INSTALLATION CERTIFICATES


[ElectriciansForums.net] ELECTRICAL INSTALLATION CERTIFICATES
 
Perhaps they want to see your design calcs although if the figures used are from the BBB or OSG no lengthy design calcs should be necessary!
May have to ask your inspector to be more specific!
 
Were they expecting to see the 80% figure of 0.69 ohms in the max permitted box?
The 2nd one is a tad close but within it.
Looking at the 2nd certificate, the other thing that might be viewed as suspicious is that by deduction the first two circuits suggest a Ze of 0.21 ish ohms and the 3 phase circuit suggests a Ze of 0.52 ohms. Something doesn't quite add up?
 

Reply to ELECTRICAL INSTALLATION CERTIFICATES in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
440
It applies to commercial if it shares the same supply as a dwelling.
Replies
4
Views
549

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top